584,837 active members*
4,824 visitors online*
Register for free
Login
Results 1 to 1 of 1
  1. #1

    Chiller Flushing Kit For Optimal Performance of the Laser Cooling System

    Water Flushing Procedure
    The purpose of these procedures is to make sure that new water and chemicals are installed in the chiller every three months for optimal performance of the laser cooling system. In addition, every sixth month the cooling system is also flushed of all debris and unwanted chemicals.

    Every 3rd month:
    Replace water by using these steps:

    Drain all the water in the tank
    Fill with new distilled water
    Add 0.5 gal of ISOGUARD per 50 gal of distilled water used
    Add 5 oz. of GAX-26 per 50 gal of distilled water used
    Every 6th month
    Replace water by using these steps:

    Drain all the water in the tank
    Fill tank with tap water and 0.5 gal of CITRONOX per 50 gal of water.
    Run the chiller for 6 hours with high voltage on
    a. Drain all the water in the tank
    b. Fill the tank with tap water only

    c. Run the chiller for 10 minutes

    d. Repeat steps a through c at least 3 times.

    5. This will flush the tank and the lines of unwanted debris and chemicals.

    6. With the tank empty, fill the tank using the “Every 3rd month” instructions.

    For More info - https://mglaser.com/products/chiller-flushing-kit
    Last edited by mglaser112; 09-25-2018 at 07:16 AM.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •