    Spindle Cable from VFD Question

    Hi if anyone can help, I have a machine running a 2.2kW HY spindle and it is using a 16 AWG 4C Shielded Cable (600v) and has been working fine for two years now. I am building a bigger machine and my supplier has run out and is not getting more and I am having trouble finding it in this rural area. However I am able to get 16 AWG 2C Shielded cable and I am wondering if a double run of this from the VFD would induce any problems?

    Thanks

    Luke

  2. #2
    Join Date
    Jun 2011
    Posts
    692

    Re: Spindle Cable from VFD Question

    Yes, you're likely to see noise issues by running your motor phases through 2 separate cables.
    You would be better off with 4 single conductor wires, twisting the 3 for the motor phases together, and running the ground along side them in some braid. Spindle wiring really should be shielded though, and that's tough to do without the proper cable.

  3. #3
    Join Date
    Jan 2005
    Posts
    15362

    Re: Spindle Cable from VFD Question

    Quote Originally Posted by robotintheforest View Post
    Hi if anyone can help, I have a machine running a 2.2kW HY spindle and it is using a 16 AWG 4C Shielded Cable (600v) and has been working fine for two years now. I am building a bigger machine and my supplier has run out and is not getting more and I am having trouble finding it in this rural area. However I am able to get 16 AWG 2C Shielded cable and I am wondering if a double run of this from the VFD would induce any problems?

    Thanks

    Luke
    You can buy your cable from IGUS the cable you want is CF6-15-04

    They are in Canada if that is where you are, here is one contact in BC

    mobile:
    1-604-316-7607
    Fax:
    1-905-760-8688
    E-Mail:
    [email protected]
    Mactec54

  4. #4
    Join Date
    Jan 2005
    Posts
    15362

    Re: Spindle Cable from VFD Question

    Quote Originally Posted by skrubol View Post
    Yes, you're likely to see noise issues by running your motor phases through 2 separate cables.
    You would be better off with 4 single conductor wires, twisting the 3 for the motor phases together, and running the ground along side them in some braid. Spindle wiring really should be shielded though, and that's tough to do without the proper cable.
    Open braid is of not use what's so every for a VFD Drive installation, 3 tightly twisted wires would be better by them selves if he has no other options
    Mactec54

Similar Threads

  1. cable chain question
    By reeser in forum DIY CNC Router Table Machines
    Replies: 6
    Last Post: 03-31-2012, 06:28 PM
  2. quick cable question.....
    By SSN Vet in forum Benchtop Machines
    Replies: 10
    Last Post: 03-16-2009, 01:12 AM
  3. PDA com cable question
    By pieface in forum DNC Problems and Solutions
    Replies: 1
    Last Post: 03-17-2006, 01:02 AM
  4. PDA com cable question
    By pieface in forum Uncategorised MetalWorking Machines
    Replies: 0
    Last Post: 01-11-2006, 04:14 PM
  5. Encoder Cable Question(s)
    By murphy625 in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 03-06-2005, 09:00 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •