    LOADING PARAMETERS INTO CONTROL 0-MB

    Dear friends,

    So far we have tried every possible way to reload parameters after a main board replacement. Sadly we have not been able to do so, because the control will not allow us to INPUT none of these parameters. Not even the 900 group. The only value we can input is TOOL OFFSETS.

    One thing I have noticed recently is what I am showing on the attached pictures. The new board does not show the bottom line. I wonder if anyone here had gone through the same scenario and found a way out. It´s been weeks already since this machine went down on us. We will appreciate any help.

    Flex.

  2. #2
    Join Date
    May 2016
    Posts
    526

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Is your parameter write switched on ?

  3. #3
    Join Date
    May 2014
    Posts
    174

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Quote Originally Posted by mbservice View Post
    Is your parameter write switched on ?
    Are you referring to this keyed switch labelled as "Program Protect" in our machine? (see picture)
    Attached Thumbnails Attached Thumbnails MISSING INFO 3.jpg  

  4. #4
    Join Date
    Apr 2017
    Posts
    9

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    No
    In second page of parameters you have :
    Put pwe to 1 to unlock




    Envoyé de mon iPhone en utilisant Tapatalk

  5. #5
    Join Date
    May 2014
    Posts
    174

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Quote Originally Posted by olivc View Post
    No
    In second page of parameters you have :
    Put pwe to 1 to unlock




    Envoyé de mon iPhone en utilisant Tapatalk
    Yes it is.

  6. #6
    Join Date
    Apr 2017
    Posts
    9

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    You have to input 900 parameters in manual

    It do procedure to restore parameters but it’s un french, if it can help you




    Envoyé de mon iPhone en utilisant Tapatalk

  7. #7
    Join Date
    Apr 2017
    Posts
    9

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    For the bellow of menu, it’s certainly diagnostic parameters about manufacturer

    On my supermax, i have to input 900 parameters and some diagnostics parameters


    Envoyé de mon iPhone en utilisant Tapatalk

  8. #8
    Join Date
    Apr 2017
    Posts
    9

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    You have alsow to open program protect key to enable dnc prog input


    Envoyé de mon iPhone en utilisant Tapatalk

  9. #9
    Join Date
    May 2014
    Posts
    174

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Quote Originally Posted by olivc View Post
    For the bellow of menu, it’s certainly diagnostic parameters about manufacturer

    On my supermax, i have to input 900 parameters and some diagnostics parameters


    Envoyé de mon iPhone en utilisant Tapatalk
    Yes. Problem here is that our controller will not allows us to INPUT any parameters at all. so we cannot load 900 parameters manually. We have tried everything we know, but like I am pointing out on my original post, what´s very suspicious is the missing bottom line of characters in the screen. We believe that is some good indicators of something wrong with the code. EPROM, MEMORY, FIRMWARE? We don´t know.

  10. #10
    Join Date
    Apr 2017
    Posts
    9

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    For me missing Line is diagnostic config.
    Do you have a save of diagnostic?

    When you put pwe=1 (in imd) you have an error ?


    Envoyé de mon iPhone en utilisant Tapatalk

  11. #11
    Join Date
    Apr 2017
    Posts
    9

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Normely to modifie parameters in manual on 0m, you only have to put pwe to 1


    Envoyé de mon iPhone en utilisant Tapatalk

  12. #12
    Join Date
    Nov 2012
    Posts
    145

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Isn’t the switch in the electrical cabinet

  13. #13
    Join Date
    Feb 2012
    Posts
    126

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    The botom line is likely missing as the softkey menu must be enabled by a paramater. On the zero it's an option.

  14. #14
    Join Date
    May 2016
    Posts
    526

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    No it sounds like your parameter write enable is switched off
    What control is that

  15. #15
    Join Date
    Apr 2009
    Posts
    1379

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    it says right in the heading: CONTROL 0-MB
    PROGRAM PROTECT key is immaterial for parameters.
    PWE is 'ON'
    He has no sub-cpu
    Masterboard has been replaced: no difference

  16. #16
    Join Date
    Jan 2006
    Posts
    61

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    I'm wondering if the machine may be in hard overtravel. If so, you must keep the OT bypass and start button pressed while you manually input the 900's. The screen that doesn't have the bottom line is indicating MDI mode.

  17. #17
    Join Date
    Dec 2009
    Posts
    952

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    can you say if diagnose X 21.4 is 0?

  18. #18
    Join Date
    May 2014
    Posts
    174

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Quote Originally Posted by zavateandu View Post
    can you say if diagnose X 21.4 is 0?
    Yes. It toggles between 1 and 0 whenever I activate E-Stop PB.

  19. #19
    Join Date
    May 2014
    Posts
    174

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Quote Originally Posted by tom o View Post
    Isn’t the switch in the electrical cabinet
    Hello Tom, To be honest, I have not looked so widely for a switch. I had no idea there could be one but I do not discard it at all, since this is a mill from 1986 that even has a TAPE READER unit. which of course we do not use. It looks like a piece of museum. Thanks for the heads up! I will let you know if I find something,

    flx

  20. #20
    Join Date
    May 2014
    Posts
    174

    Re: LOADING PARAMETERS INTO CONTROL 0-MB

    Quote Originally Posted by regina View Post
    The botom line is likely missing as the softkey menu must be enabled by a paramater. On the zero it's an option.
    Hello Regina. That´s very interesting! and please tell me, how to get to that parameter and what´s the proper procedure to change it and enable softkeys? Thank you!

Page 1 of 2 12

Similar Threads

  1. Loading parameters on 18M control
    By peloflex in forum Fanuc
    Replies: 4
    Last Post: 04-13-2017, 03:09 PM
  2. down loading parameters 18M
    By TurboCare in forum Fanuc
    Replies: 4
    Last Post: 01-01-2016, 09:53 AM
  3. loading parameters help please!
    By KyleEnright in forum Daewoo/Doosan
    Replies: 1
    Last Post: 10-07-2014, 07:44 PM
  4. UP loading parameters to the 5T
    By Paul Pippenger in forum Fanuc
    Replies: 5
    Last Post: 01-21-2009, 09:27 AM
  5. Replies: 12
    Last Post: 10-20-2008, 08:30 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •