    daewoo puma 240c year 2004

    help me.
    I Have a daewoo puma 240c lathe machine with fanuc oi-tb control.
    There a alarm which is not reset
    506 and 507 over travel alarms in both - and + in both axis.
    thanks help me
    Last edited by mankoo43; 01-27-2019 at 05:14 PM.

  2. #2
    Join Date
    Mar 2003
    Posts
    2932

    Re: daewoo puma 240c year 2004

    I believe you can hold down the "P" and "CAN" buttons while powering up the machine. This should temporarily ignore the overtravel alarms and allow you to move (HANDLE or JOG) the offending axis away from it's limit. I haven't done this myself in a loooooong time, so "caveat emptor".

  3. #3
    Join Date
    May 2016
    Posts
    526

    Re: daewoo puma 240c year 2004

    Quote Originally Posted by dcoupar View Post
    I believe you can hold down the "P" and "CAN" buttons while powering up the machine. This should temporarily ignore the overtravel alarms and allow you to move (HANDLE or JOG) the offending axis away from it's limit. I haven't done this myself in a loooooong time, so "caveat emptor".
    You should be able to jog off the overtravels prior to referencing
    You may have to jog off the interlocks and then re-boot holding down P and CAN

  4. #4
    Join Date
    Mar 2003
    Posts
    2932

    Re: daewoo puma 240c year 2004

    Mankoo43 says he has + AND - O.T. alarms in both axes. I don't believe you can move an axis with both + and - O.T. alarms.

  5. #5

    Re: daewoo puma 240c year 2004

    506 & 507 are HARD overtravel and P CAN will not work on these alarms. You lost your 24V that feed these switches. You will need your electrical prints to see where you lost it.

  6. #6
    Join Date
    Feb 2013
    Posts
    788

    Re: daewoo puma 240c year 2004

    P-Can is for Soft over travel.

    Alarm 506 = Over Travel: +n (Hardware)
    Alarm 507 = Over Travel: -n (Hardware)

    Content: Exceeded the n-th axis hardware OT. Check 24v to overtravel limit switch. Move off of hard limit switch. The signal is active-low, requiring 24v applied to deactivate, so a loss of 24v or tripping of the switch causes the alarm.

    Troubleshooting:
    Check 24v to overtravel limit switch. Move off of hard limit switch.Check function of switch.

    Specific to your case: Press and hold the Blue Alarm RESET button, if Machine Ready is allowed and hydraulics are able while blue button is pressed, then the problem is in the switch/switches. (the blue button only provides a path around the switches and over-torque clutch inputs...it uses the same 24v. If blue button does nothing, check the voltage supplied to switches as well as the input they arer being read at.
    Doosan Service Technician
    [email protected] O:973-618-2461 M:973-803-9479

  7. #7
    Join Date
    Feb 2013
    Posts
    788

    Re: daewoo puma 240c year 2004

    If given a serial number, I can describe where to check, via the electrical print.