Originally Posted by
mactec54
Where you show the Ground wire looping around the VFD you can not do that and as for the shaft Grounding that should be direct to the Body of the spindle not wires needed
You need to Have a single point ( Star Ground ) where all your Ground wires attach the Main Ground should be attached to this Star Ground Point then you VFD Ground Goes from this point to the VFD Drive, the Spindle Ground can connect to the VFD Ground Terminal or the Star Ground Point, But no loops are aloud
Do you have your VFD Mounted in a Cabinet if so the Metal mounting plate becomes the Ground Plane once you Create a Star Point Ground on this panel
So you have many choices for Ground wire Termination, but all will be at one point ( Star Ground ) bonded to the metal Ground Plane ( Metal Mounting Plate )