585,987 active members*
4,623 visitors online*
Register for free
Login
Results 1 to 7 of 7
  1. #1

    Question E-Stop and Safety Relay Questions

    My DIY build will use a simple AC router. So on the AC side I'll have an e-stop button controlling a relay connected to the router.

    So on the stepper drive side do you interrupt the ac to the PSU or the DC supply side, or both?

    Is a single pole enough for the router AC side or should you use a 2-pole?

  2. #2
    Join Date
    Mar 2003
    Posts
    35538

    Re: E-Stop and Safety Relay Questions

    If it's a 120V router, then you just need to cut power to the hot side.

    Never cut DC power, you'll fry the drive.

    Thgere's really no point in killing power to the stepper drives, as steppers will stop as soon as the step pulses stop, which is much sooner than the capacitors in the power supply drain.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  3. #3
    Join Date
    Mar 2017
    Posts
    411

    Re: E-Stop and Safety Relay Questions

    I would cut AC power to anything that moves. Not, just the router but the stepper drive also. I am also assuming that you are using the E-Stop switch to send a signal to the motion control board too.

    You can never assume that things will stop moving because you sent them a signal. Cut their power as well.

    As far as the disconnect relay, it should be one intended for the disconnect purpose. Also, please correct me if I am wrong someone, a 20 Amp 3 phase contactor is not rated for 20 Amps on each leg, it is 20 Amps total.

    Page 3.
    https://literature.rockwellautomatio...d556_-en-p.pdf

  4. #4
    Join Date
    May 2005
    Posts
    3920

    Re: E-Stop and Safety Relay Questions

    If you read further contact ratings are per pole! However don’t assume that all poles are the same they can have different ratings though you don’t see that much on safety relays. It is always a good idea to reference documentation whenever possible, If not documentation the devices labeling.

    As a side note it is a mistake to believe safety relays make a machine more reliable. At work they are the most commonly replace item in the control cabinets. They MIGHT make for a safer machine but even here there are always issues that require careful consideration.

    Quote Originally Posted by maxspongebob View Post
    I would cut AC power to anything that moves. Not, just the router but the stepper drive also. I am also assuming that you are using the E-Stop switch to send a signal to the motion control board too.
    Yes cut AC power but also drive enables.
    You can never assume that things will stop moving because you sent them a signal. Cut their power as well.

    As far as the disconnect relay, it should be one intended for the disconnect purpose. Also, please correct me if I am wrong someone, a 20 Amp 3 phase contactor is not rated for 20 Amps on each leg, it is 20 Amps total.
    It is always possible that I’ve missed a relay where this is true but all that I’ve worked with are rated on a per contact basis. What you have to be careful about here is that a relay (especially 3 phase power relays) will have three sets of contacts rated for power and one or more rated for “pilot” duty. The safety relays Ive worked with generally have contacts all rated the same per pole. Heavy current switching is handled by external relays. That being said I would not be surprised at all to find safety relays with high power contacts.
    I’m not sure what you are referencing on page 3. Nothing about contact capacity is mentioned there.

  5. #5
    Join Date
    Sep 2005
    Posts
    1740

    Re: E-Stop and Safety Relay Questions

    A contractor is rated per amps per contact, so a 20 amp 3 phase contractor is rated the same. Never ever break the output legs of a VFD going to a 3 phase motor or you will fry the VFD/ Inverter. Best safety switch on a machine is the guy/gal running it.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  6. #6
    Join Date
    Jan 2005
    Posts
    15362

    Re: E-Stop and Safety Relay Questions

    Quote Originally Posted by Project_Hopeless View Post
    My DIY build will use a simple AC router. So on the AC side I'll have an e-stop button controlling a relay connected to the router.

    So on the stepper drive side do you interrupt the ac to the PSU or the DC supply side, or both?

    Is a single pole enough for the router AC side or should you use a 2-pole?
    If you are using 120v then you only need a single pole if you at using 240v then you need a 2 pole
    Mactec54

  7. #7
    Join Date
    Dec 2003
    Posts
    24221

    Re: E-Stop and Safety Relay Questions

    Quote Originally Posted by wmgeorge View Post
    Never ever break the output legs of a VFD going to a 3 phase motor or you will fry the VFD/ Inverter. Best safety switch on a machine is the guy/gal running it.
    It will if output power is present, I have actually done it with two contactors on the output for two motors that operated alternately, but used the At-Zero-Speed output to interlock the two contactors to ensure they did not switch when output was present.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. UB1 with Safety relay
    By vrasak in forum UCCNC Control Software
    Replies: 0
    Last Post: 01-07-2019, 11:01 AM
  2. safety relay and amc drives
    By pitchblack650 in forum Servo Motors / Drives
    Replies: 6
    Last Post: 12-28-2014, 02:05 PM
  3. Using a solid state relay as a main stop relay
    By garagefela in forum CNC Machine Related Electronics
    Replies: 4
    Last Post: 02-26-2010, 11:27 PM
  4. MORI SL253B 500 safety relay
    By mr pitt in forum Mori Seiki lathes
    Replies: 3
    Last Post: 07-19-2008, 05:50 PM
  5. Dold Safety Relay - any use?
    By TravisR100 in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 01-29-2007, 12:52 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •