    Getting single phase 220v and 110v from 3 phase 220v

    Hello,

    Looking for suggestions to get single phase 220v for my servo drives as well as 110v single phase for the PC running the machine.

    Any suggestions are appreciated!

    Thanks

  2. #2
    Join Date
    Dec 2013
    Posts
    5717

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Assuming you are in North America, what is your 3 phase voltage? 208, 240, 480? There is no 220V in North America.

    I'm splitting hairs here because each case is different. See here https://ctlsys.com/support/electrica..._and_voltages/
    Jim Dawson
    Sandy, Oregon, USA

  3. #3
    Join Date
    Aug 2013
    Posts
    76
    Quote Originally Posted by Jim Dawson View Post
    Assuming you are in North America, what is your 3 phase voltage? 208, 240, 480? There is no 220V in North America.

    I'm splitting hairs here because each case is different. See here https://ctlsys.com/support/electrica..._and_voltages/
    Will likely be 240v from an American rotory phase converter.

  4. #4
    Join Date
    Aug 2009
    Posts
    1570

    Re: Getting single phase 220v and 110v from 3 phase 220v


  5. #5
    Join Date
    May 2013
    Posts
    480

    Re: Getting single phase 220v and 110v from 3 phase 220v

    you likely do not need 120vac for your computer. many are 100-260vac, they take the incoming ac and convert it to 400 volts dc.

    the older computer power supplies have a switch you need to set for 120/240 operation. get it wrong and it blows up.


    you will need a transformer if you really do need 120 from from a 240v source.

    in the case of your rotary phase converter you have 120vac from line 1 and 2 to neutral. line 3 will read 208 volts to neutral. you can buy a 5 pin plug to handle that correctly but there is no guarantee that everyone has 120v line to ground on two of the phases. it could be 138 on all three phases, or it could be 120/208 for high leg delta (electrically a rotary phase converter and high leg delta is the same thing) so if your machine ever gets plugged into someone else's system there is no guarantee they had it wired up the same way, so there is a 1 in 3 chance you end up sending 208 into your 120v system.

    corner grounded delta won't have a neutral so there is no chance of your machine ever being plugged into that if you wire it up with a 5 pin plug.

    nema L21-20R for example.

    i'm not aware of plugs specifically for high leg delta (aka center tapped delta)

  6. #6
    Join Date
    Mar 2003
    Posts
    35538

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Will likely be 240v from an American rotory phase converter.
    Do you have single phase 240V available directly? If so, just run a 4 wire cord like a dryer cord, which will give you both 120V and 240V.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  7. #7
    Join Date
    Jan 2005
    Posts
    15362

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by PIVOTALCUSTOMS View Post
    Will likely be 240v from an American rotory phase converter.
    The RPC most likely will smoke the servo drives, servo drives in general don't like RPC's a lot of servo drives will run on 220/240v single phase so what do you have for servo drives
    Mactec54

  8. #8
    Join Date
    Aug 2009
    Posts
    1570

    Re: Getting single phase 220v and 110v from 3 phase 220v


  9. #9
    Join Date
    Dec 2013
    Posts
    5717

    Re: Getting single phase 220v and 110v from 3 phase 220v

    You need the RPC to run your spindle? And if that's the case, why are you using single phase servo drives?

    But, coming off of the RPC you have the two normal single phase hot legs and the manufactured leg. I would use a 240/120 transformer across the 240 legs to derive the 120V, or power the computer from a completely separate circuit so you can use it without the RPC running. This is the way my lathe is set up.

    Since you're using single phase servo drives, also make sure they are wired to the 240V hot legs and not to the manufactured leg from the RPC.
    Jim Dawson
    Sandy, Oregon, USA

  10. #10
    Join Date
    Aug 2009
    Posts
    1570

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by PIVOTALCUSTOMS View Post
    Hello,

    Looking for suggestions to get single phase 220v for my servo drives as well as 110v single phase for the PC running the machine.

    Any suggestions are appreciated!

    Thanks
    Call a Pro...maybe Maytag repairman local

  11. #11
    Join Date
    Aug 2013
    Posts
    76

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Sorry I mis-spoke, I am actually going to be using the PT-355 from Phase Perfect. I was originally looking at the ARC but the phase perfect seemed a much better application for the CNC.

    Anyhow, My retrofit has two single phase 220 Servo Drives on X and Y and a 220 three phase on the larger Z axis. The spindle Drive is also three phase.

    The PT-355 describes its output as follows:

    The converter shall be based on a double-IGBT conversion design, rectifying the
    incoming AC power to DC, then generating a third AC voltage which is added to
    the two legs of the single-phase service, producing balanced three-phase power
    in a closed delta configuration with a center-tap ground between two of the legs.

    This is where Im a bit unsure, I considered pulling a leg for 110 like i have done in the past on the RPC but i wasn't able to find alot of info on a Closed Delta Config, so im unsure if thats doable?

    If not is there a transformer config that can go 3 phase to 220 with neutral?

    Thanks for the info and sorry for the hasty post and lack of info.

  12. #12
    Join Date
    Dec 2013
    Posts
    5717

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Well that changes things a bit. I think it's time for a chat with Phase Perfect tech support. Reading through the manual it looks to me like 120V could be derived from one leg to neutral, but I'm having a bit of a hard time getting my head around exactly what it says. Same with using two legs as a 240V single phase output, it seems like it would work but I'm not sure. I would prefer that they show a diagram of the wiring for those configurations. Like I said, talk to tech support for a real answer.

    Look at the Three Phase Four Wire Delta diagram from the link I posted above.
    Jim Dawson
    Sandy, Oregon, USA

  13. #13
    Join Date
    Aug 2013
    Posts
    76

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Thanks Jim,

    I will definitely give them a call tomorrow, thats where I was at as well but I wasn't sure if that was just due to my more limited understanding of all of this or if there documentation wasn't 100% clear.

    I will report back with their answers.

  14. #14
    Join Date
    Jan 2005
    Posts
    15362

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by Jim Dawson View Post
    You need the RPC to run your spindle? And if that's the case, why are you using single phase servo drives?

    But, coming off of the RPC you have the two normal single phase hot legs and the manufactured leg. I would use a 240/120 transformer across the 240 legs to derive the 120V, or power the computer from a completely separate circuit so you can use it without the RPC running. This is the way my lathe is set up.

    Since you're using single phase servo drives, also make sure they are wired to the 240V hot legs and not to the manufactured leg from the RPC.

    He would need a Neutral wire to get 120v supply from the 240v source

    Depending on what size his spindle Hp is he may not need a RPC for his machine at all, so he needs posts what his spindle requirement's are and does it have a VFD Drive
    Mactec54

  15. #15
    Join Date
    Aug 2013
    Posts
    76
    Quote Originally Posted by mactec54 View Post
    He would need a Neutral wire to get 120v supply from the 240v source

    Depending on what size his spindle Hp is he may not need a RPC for his machine at all, so he needs posts what his spindle requirement's are and does it have a VFD Drive
    The spindle motor is a 5.5 kw 3phase servo spindle motor running a 3 phase pulse/direction drive.


    The servo for my z is also a dedicated 3phase drive.
    So as far as I can tell 3 phase is required.

    So after chatting with Phase Technologies the output is closed Delta 3 wire phase to phase 1% voltage with on leg being high phase to ground...

    The 220v servo drives are currently running 2 hot legs of 220v service no neutral in my test setup( the inputs are designed for oversees power 1 hot 220v leg 1 neutral)

    So could I in theory just run those from 2 low legs to ground with 220v between phase?

    That just leaves me with the 110v issue

  16. #16
    Join Date
    Jan 2005
    Posts
    15362

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by PIVOTALCUSTOMS View Post
    The spindle motor is a 5.5 kw 3phase servo spindle motor running a 3 phase pulse/direction drive.


    The servo for my z is also a dedicated 3phase drive.
    So as far as I can tell 3 phase is required.

    So after chatting with Phase Technologies the output is closed Delta 3 wire phase to phase 1% voltage with on leg being high phase to ground...

    The 220v servo drives are currently running 2 hot legs of 220v service no neutral in my test setup( the inputs are designed for oversees power 1 hot 220v leg 1 neutral)

    So could I in theory just run those from 2 low legs to ground with 220v between phase?

    That just leaves me with the 110v issue
    You need a neutral for 120v single phase which you can split from any of you main 240v supply if you live in NA then you have120 / 240v single phase supply not 220v


    Don't believe what they are telling you about the RPC, there is not an RPC made, does not matter what brand or manufacture they will not be even close to 1% even the CNC grade RPC


    No you can not run the low legs to Ground lots of smoke and Brakers would trip if you short a live wires of anything


    Now if you where talking Phase Perfect then there digital phase converter can easy give you clean 3Ph power @ 98% efficiency


    Who is the manufacture of the servo drive most 3Ph servo drives will run on single yours would be at the top of the range for single phase though but worth a try
    Mactec54

  17. #17
    Join Date
    Jan 2005
    Posts
    15362

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by PIVOTALCUSTOMS View Post
    The spindle motor is a 5.5 kw 3phase servo spindle motor running a 3 phase pulse/direction drive.


    The servo for my z is also a dedicated 3phase drive.
    So as far as I can tell 3 phase is required.

    So after chatting with Phase Technologies the output is closed Delta 3 wire phase to phase 1% voltage with on leg being high phase to ground...

    The 220v servo drives are currently running 2 hot legs of 220v service no neutral in my test setup( the inputs are designed for oversees power 1 hot 220v leg 1 neutral)

    So could I in theory just run those from 2 low legs to ground with 220v between phase?

    That just leaves me with the 110v issue
    Are that makes a big difference Phase Perfect is the way to go if you need 3ph power I have a PT380 you could get them to add a Neutral terminal block so you could run a Neutral for a 120v supply as well I did not but did not have a need for 120v

    You would take the 120v from one Hot leg that feeds the Phase Perfect and the Neutral and Ground would give you a normal 120v supply
    Mactec54

  18. #18
    Join Date
    Dec 2013
    Posts
    5717

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by mactec54 View Post

    Don't believe what they are telling you about the RPC, there is not an RPC made, does not matter what brand or manufacture they will not be even close to 1% even the CNC grade RPC
    You are correct in that you can't buy one off the shelf. But it's possible to build one Here is a picture of the panel meters on mine 1.01% or better under most operating conditions. T1-T3 is about 255 unloaded, but settles right down under any load. But a Phase Perfect would probably be better.

    239, 237, 239, 236 if you can't read the meters.
    Jim Dawson
    Sandy, Oregon, USA

  19. #19
    Join Date
    Sep 2005
    Posts
    1740

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Very impressive Jim. If the OP needs 5 amps or so 120 vac just install a transformer. We did it all the time on 3 phase MCC that used 120 vac for controls. FYI most PCs today will run on either 120 or 240 vac, please check your power supply!
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  20. #20
    Join Date
    Jan 2005
    Posts
    15362

    Re: Getting single phase 220v and 110v from 3 phase 220v

    Quote Originally Posted by Jim Dawson View Post
    You are correct in that you can't buy one off the shelf. But it's possible to build one Here is a picture of the panel meters on mine 1.01% or better under most operating conditions. T1-T3 is about 255 unloaded, but settles right down under any load. But a Phase Perfect would probably be better.

    239, 237, 239, 236 if you can't read the meters.

    Looks good but still not the at 1% if your wild leg is 255 then you are around 6.7% no point in showing something that others can't have or likely to achieve, but still in reality is no better than a CNC rated RPC
    Mactec54

Page 1 of 2 12

Similar Threads

  1. Replies: 34
    Last Post: 08-17-2021, 07:16 AM
  2. 110v VFD, 220v, 1 phase, 3 phases - I'm kind of lost
    By Biggs427 in forum Spindles / VFD
    Replies: 7
    Last Post: 06-16-2017, 02:52 PM
  3. Bridgeport R2E3 delima, 220v VFD 3 phase Versus 220V Single Phase
    By ronderkis in forum Bridgeport / Hardinge Mills
    Replies: 7
    Last Post: 03-25-2015, 04:01 AM
  4. Replies: 2
    Last Post: 06-20-2014, 05:24 AM
  5. Replies: 12
    Last Post: 10-13-2009, 03:53 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •