    Question Spindle heats up

    Hello, i bought Isacon Power Control Tech A2 series VFD and new spindle ( parameters of both items can see in attachment). Connected VFD to single-phase 220v and three wires of the motor to U, V, W. Everything seems to work fine but the problem is that spindle heats up very fast (cant touch with hands). I noticed that inverter output is 10A but on spindle it is 5A mark. Can this be a problem? Are this 2 items compatible at all? Thank you

  2. #2
    Join Date
    Sep 2005
    Posts
    1740

    Re: Spindle heats up

    You have to set up the VFD for your spindle, would running it at 10 amp vs 5 on nameplate be a problem, yes. My guess you have already overheated the windings and its next stop could be the dump. Find your owners manual and set the parameters, or contact the people you purchased it from.
    BTW is it air or water cooled and if water was it connected to same?

    Running this spindle slower than 100 Hz can damage it and slower that 130 Hz if its air cooled will overheat it.

    Mactec 54 can help you.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  3. #3
    Join Date
    Jun 2019
    Posts
    2

    Re: Spindle heats up

    Sorry i didnt mention but i set up VFD for this spindle using manual i had in box with VFD, but it is no option to change amps in VFD settings.. It is Air cooled spindle so i was trying to test it on 200+Hz. But i also noticed that spindle starts to heat up a little right after i turn on VFD ( without spinning )

    Seller told i should use spindle 300+Hz so it cool down, but i didnt noticed any big changes and it seems weird. So i think maybe they just sold me 2 incompatible items

  4. #4
    Join Date
    Sep 2005
    Posts
    1740

    Re: Spindle heats up

    Sure there are perimeters to change for amps, if not send it back.
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

  5. #5
    Join Date
    Mar 2017
    Posts
    926

    Re: Spindle heats up

    Have you checked that the shaft fan is working?

    Those shaft fan spindled only self cool properly at higher speeds but if it is working properly, it should not overheat so quickly without a heavy load.

  6. #6
    Join Date
    Jan 2005
    Posts
    15362

    Re: Spindle heats up

    Quote Originally Posted by Bublcsh View Post
    Hello, i bought Isacon Power Control Tech A2 series VFD and new spindle ( parameters of both items can see in attachment). Connected VFD to single-phase 220v and three wires of the motor to U, V, W. Everything seems to work fine but the problem is that spindle heats up very fast (cant touch with hands). I noticed that inverter output is 10A but on spindle it is 5A mark. Can this be a problem? Are this 2 items compatible at all? Thank you
    You have not set the Correct Parameters for your spindle, it is 400Hz and can not be set for any other Hz settings I have a set of parameters for that VFD Drive but won't have access for a few days, if you can't find the correct Parameters to set don't run the Spindle or you will fry if
    Mactec54

  7. #7
    Join Date
    Sep 2005
    Posts
    1740

    Re: Spindle heats up

    Quote Originally Posted by Bublcsh View Post
    Sorry i didnt mention but i set up VFD for this spindle using manual i had in box with VFD, but it is no option to change amps in VFD settings.. It is Air cooled spindle so i was trying to test it on 200+Hz. But i also noticed that spindle starts to heat up a little right after i turn on VFD ( without spinning )

    Seller told i should use spindle 300+Hz so it cool down, but i didnt noticed any big changes and it seems weird. So i think maybe they just sold me 2 incompatible items
    Try this > https://www.cnczone.com/forums/spind...131-forum.html
    Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP

Similar Threads

  1. Replies: 3
    Last Post: 10-19-2018, 05:12 PM
  2. Replies: 39
    Last Post: 01-09-2017, 06:26 AM
  3. AM882 heats motors up
    By Antennas in forum Leadshine
    Replies: 2
    Last Post: 05-10-2015, 02:26 AM
  4. Replies: 5
    Last Post: 07-19-2013, 05:16 AM
  5. HELP Power supply broken... Bridge rectifier smokes... Coil heats up.
    By Delanoman in forum DNC Problems and Solutions
    Replies: 3
    Last Post: 04-07-2009, 04:19 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •