Hi, i just got a new spindle and the vfd but i can't set it up, the vfd it is a chines model Fuling BD-600 serie it is a 5.5 kw 380 ac 300 Hz and the spindle it is 4.5 kw 9 amp 24000 rpm 800 Hz can some one help. thanks
Hi, i just got a new spindle and the vfd but i can't set it up, the vfd it is a chines model Fuling BD-600 serie it is a 5.5 kw 380 ac 300 Hz and the spindle it is 4.5 kw 9 amp 24000 rpm 800 Hz can some one help. thanks
Is your full part number BD600-3R7G/5R5P-4
And what won't set up?
Jim Dawson
Sandy, Oregon, USA
Part number BD 613-5R5-4
I was able to run the spindle but it only turn really slow and when i turn the potentiometer give error and stop
I can only set to 320 Hz and the spindle it is 800 Hz, I'm really lost with this set up.
I can't find a manual for that part number. Do you have 380V 3 phase power? From what I can find so far it requires 3 phase input.
Did you set the motor parameters in the VFD?
Jim Dawson
Sandy, Oregon, USA
yes , I have 380v 3 phase
yes i put the incorrect info the vfd it is 3000Hz
the error that give me it is e032
Last edited by DonPapp; 10-01-2019 at 12:38 AM.
I can't find a manual for that drive online, do you have a link to a manual?
Jim Dawson
Sandy, Oregon, USA
www.chinafuling.com
You need either a different vfd, or different spindle. They need to match in the hz and voltage.
I'll try
I can't snap a photo but this is what it is on it:
model: BD613-5R5-4
input: 3PH 380V 50/60Hz
output: 3PH 0~380V 0~3000Hz
power: 5.5 Kw 13.0 A
S/N 00 6131AB1H41819331900
Here is some Parameters you need to set, you may have to do a reset the VFD Drive if you have set other Parameters, once Reset then use these Parameter settings
First select operation instruction channel (F00.01) as keypad instruction channel.
F00.03=800
F00.04=800
F00.05=120
F00.10=800
F00.12=10 ( Adjustable )
F00.13=10 ( Adjustable )
F00.17=8
F02.01=5.5 ( Motor Power )
F02.02=800 ( Motor Frequency )
F02.03=24000 ( Max Motor speed )
F02.04=380 ( Motor voltage )
F02.05=9 ( Max Motor Amps )
These Parameters must all be set, then you can do a Auto Tune with Parameter F02.37=1
F02.37= 1 (dynamic self-learning), and then press “RUN” on control panel, it will then calculate
other settings related to your Spindle motor
Mactec54
Two more Parameters if you have not found them
Reset= F00.28=1 it will return to ( 0 ) once complete
You may also have to set this Parameter for motor model type also
F00.27= ( Motor P Type variable torque load=2 )
( Motor G Type constant torque load=1 )
Mactec54
Hi, I try to input the setting but don't let me pass 320 Hz.
I believe that this VFD it is a counterfeit from the chines so I got a VFD best FC-5.5G-T4-B4 and all it's OK my spindle running fine at 2400 rpm.
Something is a little fishy with that motor nameplate. What is the rated RPM at 3000 Hz?
Retired Master Electrician, HVAC/R Commercial. FLA Saturn 2 4x4 CNC Router Mach4 Kimber 1911 45ACP