    Leeson SM series VFD

    I've installed a haugyang with a 3ph air compressor and it works good. But I'm in the process of retrofitting my mill with a centroid acorn controller. The motor is a leeson 2hp 3ph. the VFD is a Leeson SM series. I've looked over the schematics for the acorn. And the manual for the vfd. I'm stumped. Any help would be great. Thanks in advance.

  2. #2
    Join Date
    Dec 2013
    Posts
    5717

    Re: Leeson SM series VFD

    Which part are you stumped on?

    Look at page 17, Two Wire Start Stop Control, of the Leeson manual. Then look at the generic VFD drawing from the Centroid documents.

    The Analog VFD control from the Centroid connects to terminals 5 (+) and 2 (-)

    You only need to relay output from the Centroid to run the VFD, Terminal 1 RUN (forward), and Terminal 13A (Reverse), connect the Signal Input Reference (common) as shown on the Centroid drawing.
    Jim Dawson
    Sandy, Oregon, USA

  3. #3
    Join Date
    Dec 2016
    Posts
    27

    Re: Leeson SM series VFD

    Quote Originally Posted by Jim Dawson View Post
    Which part are you stumped on?

    Look at page 17, Two Wire Start Stop Control, of the Leeson manual. Then look at the generic VFD drawing from the Centroid documents.

    The Analog VFD control from the Centroid connects to terminals 5 (+) and 2 (-)

    You only need to relay output from the Centroid to run the VFD, Terminal 1 RUN (forward), and Terminal 13A (Reverse), connect the Signal Input Reference (common) as shown on the Centroid drawing.
    I'll Give it a try. Thank You

  4. #4
    Join Date
    Dec 2016
    Posts
    27

    Re: Leeson SM series VFD

    It worked. Terminals 1 fwd and 13A rev. Terminals 2 and 5 and 11. was also used on the VFD. 300 rpm on high pulley pulled 6.5hz and 4500 rpm pulled 80hz. About 3100 rpm wad 60hz. So Thank You, MR Jim Dawson.

  5. #5
    Join Date
    Dec 2013
    Posts
    5717

    Re: Leeson SM series VFD

    My pleasure to help out. Happy to hear it worked out.
    Jim Dawson
    Sandy, Oregon, USA

Similar Threads

  1. Replies: 4
    Last Post: 02-21-2019, 08:24 PM
  2. G0704 with 3 Phase Leeson Metric motor
    By bgriggs in forum Benchtop Machines
    Replies: 22
    Last Post: 03-15-2018, 10:52 PM
  3. Baldor or Leeson
    By dbrowning52FL in forum BobCad-Cam
    Replies: 3
    Last Post: 10-14-2015, 09:21 PM
  4. Notice- Reci improves laser tubes from V series to W series in 2012
    By Melody-gweike in forum Laser Engraving / Cutting Machine General Topics
    Replies: 6
    Last Post: 07-21-2012, 08:07 PM
  5. Apparent issue with SJ200 & Leeson 3ph 2HP motor
    By haysys in forum Phase Converters
    Replies: 31
    Last Post: 01-14-2008, 01:04 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •