Having the Power Filter will solve your problem, if you look at your VFD Drive manual it will show you this in the wiring, it is a requirement in most installs, and is what should be installed with power supplies and VFD Drives
Using the debounce will slow down the reaction time of the limit switches and Homing, so not a good fix just a band-aid the higher you go with the Debounce the slower the switched signal reacts
Mactec54
Olf G'day,
Just a quick update and thanks again for your assist. The debounce filter that I had no clue about nor what its use was for helped me further debug what was going on with my limit switches.
So earthing was ok, switches ok, replaced cable with shielded cable. My Y Axis was still doing a small samba dance of its own.
So I ended up putting on another limit switch on the opposite end of Y Axis, I have two steppers driving Y. I read somewhere on this forum that you needed to use a separate input if you want to auto lvl your gantry.
Neways, as soon as I hooked up the second limit switch for homing for the Y Axis, the Y on homing started performing the way it should. I thought maybe a coincidence so I disabled the second Y limit switch and Y Homing went back to doing a dance.
For whatever reason having Y Homing on the one limit switch with two steppers for me would not behave as it was meant too.
My problem is resolved back off works correctly, homing now ok, and I have removed debounce which is no longer required.
I'm sure it is due to operator error, I haven't done something properly somewhere.
For the moment everything is working correctly now.
Cheers and thanks for the assist.
Steve
That's another reason you where asked to post some photos of your wiring this would of been picked up by some of the more experienced builders here
Using the Debounce in this case should not of changed anything as that is for noise related problems, but you said it fixed the problem but obvious it did not in this case
Mactec54
Well posting pics of my wiring I don't think would have helped. Whatever the issue was it seemed to have removed itself by adding a second limit switch. It wasn't operating the way it was intended running in series. The debounce initially helped that the Y axis didn't do as much of a dance . Y axis. It was homing ok but was not returning the distance I had nominated eg in my case I wanted Y to retract 180mm, as I have my 4th axis mounted at the front. The left side was going ok but the right was being pulled rather than moving on its own. Over a short distance eg 5 - 10 mm it looked ok but in actual fact it wasn't that only revealed itself later.
So using the second input for whatever reason resolved my issue. Y retracts the nominated distance no more dance. Both motors working correctly left is no longer pulling right side of gantry.
Whatever the cause I learned some new things with the help of a lot of members from this forum, your good self included.
I have learned what debounce is for, that the inputs on the AXBB-E are not 11, 12 etc but instead i1, i2 I could have looked at that till the cows came home I would never have picked it up. Along side many other things.
Mactec ty for your input greatly appreciated and to everyone else who has assisted along the line since my joining cnczone.
Cheers,
Steve
You said in your first sentence you had the switches in series, this is never going to work having 2 motors to control if that is how it was setup
Glade you got it sorted most times we are all guess unless we see the whole picture
If the Debounce helped a little then there was some noise that it was canceling / helping to control
Mactec54
I had switches in series yes.. if you wouldn't mind explaining why it was never going to work with controlling two motors. I'm now assuming I guessed right (no foreknowledge) that I needed to add another switch.
An opportunity for me to learn for the future.
Cheers,
Steve
Mactec54
Matec ty for the reply,
That makes sense, thank you for taking the time to explain that much appreciated.
Steve
Summary?
Good shielding for everything. (Motors and signals)
Good star grounding for everything.
Mains filter on input.
I dare say there are more.
Cheers
Roger
I needed to put my limit switch for the right hand stepper on a separate input
That figures all right. If the 1st motor in your system left the single limit switch activated, then there would be no sensor for the 2nd motor.
Cheers