    Does wiring for limit switches need to be shielded?

    Hey G'day,

    Does the wiring for limit switches need to be shielded,

    I'm getting some strange behavior reset button will randomly enable.

    Unable to switch it off. Even using override not helping. I then disable limit switch/re enable good for a while.

    My limit switches will not work in series for whatever reason, each switch wired separately functions ok.

    There are no breaks in the wiring all seems good.

    If I use some test wire all switches test ok, doing homing routine axis by axis function ok.

    If I use the wires through the cnc loom, Y (I have a slave) the homing is interesting to say the least. One side seems to advance quicker than the other or at moments move in opposite directions to each other its a ballet dance.

    Breaking out the test wires the switch functions ok and the homing sequence is ok.

    Cheers,
    Steve

  2. #2
    Join Date
    Dec 2013
    Posts
    5717

    Re: Does wiring for limit switches need to be shielded?

    It does seem that you are picking up some electrical noise. Are you using your switches Normally Closed? That is normally reasonably noise immune, and also if a wire breaks it looks like an activated switch. It's possible that you need to shield the motor cables or at least separate the power and signal cables as much as possible. If needed, then shield the limit switch cables.
    Jim Dawson
    Sandy, Oregon, USA

  3. #3
    Join Date
    Dec 2003
    Posts
    24220

    Re: Does wiring for limit switches need to be shielded?

    Most of the causes of what you ate experiencing I have found to be lack of proper earth bonding and grounding of power commons etc to a star ground, that includes the service ground .
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    Jun 2013
    Posts
    454

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by Jim Dawson View Post
    It does seem that you are picking up some electrical noise. Are you using your switches Normally Closed? That is normally reasonably noise immune, and also if a wire breaks it looks like an activated switch. It's possible that you need to shield the motor cables or at least separate the power and signal cables as much as possible. If needed, then shield the limit switch cables.
    Hey Jim G'day,

    Thank you for the reply,

    Yes all the switches are normally closed. All the motors have shielded cables.

    I guess I will bite the bullet and rewire again. My assumption (obviously wrong) was if using Normally Closed switches it wouldn't matter.

    Laughing gently atm, my mate just called with a similar dropout issue, whenever he turns his spindle on his laptop drops connection to UCCNC. His issue was easy to fix, he doesn't like using the touch pad so he keeps attaching a wireless mouse, Every time he adds the mouse hes in trouble lol.

    He unfortunately doesnt have a solution for me. Ok back to the garage see if I have any more shielded cable left.


    Cheers,
    Steve

    Maybe I should try normally open and see if that doesn't improve things.

  5. #5
    Join Date
    Dec 2013
    Posts
    5717

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by curiosity22 View Post
    Hey Jim G'day,

    Thank you for the reply, .......

    Maybe I should try normally open and see if that doesn't improve things.
    My pleasure.

    At this point anything is worth a try.
    Jim Dawson
    Sandy, Oregon, USA

  6. #6
    Join Date
    Jun 2013
    Posts
    454

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by Al_The_Man View Post
    Most of the causes of what you ate experiencing I have found to be lack of proper earth bonding and grounding of power commons etc to a star ground, that includes the service ground .
    Al.
    I believe everything is well grounded but a valuable point to check. Thank you for the input I will look at that as well to make sure..

  7. #7
    Join Date
    Jun 2015
    Posts
    943

    Re: Does wiring for limit switches need to be shielded?

    You can use the debounce filter of the UCCNC to filter out noise on your limit switch inputs.
    You can set a few milliseconds and then those short noise spikes will be ignored by the controller.

  8. #8
    Join Date
    Jan 2005
    Posts
    15362

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by curiosity22 View Post
    Hey G'day,

    Does the wiring for limit switches need to be shielded,

    I'm getting some strange behavior reset button will randomly enable.

    Unable to switch it off. Even using override not helping. I then disable limit switch/re enable good for a while.

    My limit switches will not work in series for whatever reason, each switch wired separately functions ok.

    There are no breaks in the wiring all seems good.

    If I use some test wire all switches test ok, doing homing routine axis by axis function ok.

    If I use the wires through the cnc loom, Y (I have a slave) the homing is interesting to say the least. One side seems to advance quicker than the other or at moments move in opposite directions to each other its a ballet dance.

    Breaking out the test wires the switch functions ok and the homing sequence is ok.

    Cheers,
    Steve
    Your best choice is to add a EMI Power Filter on the input power to the VFD Drive and most of these problems will despair Here is the Filter spec's you will need it looks big in the photo but it is quite small

    TDK Lambda EMI RSEN-2030L Power Filter this needs to be mounted close to the input Power to the VFD Drive
    Mactec54

  9. #9
    Join Date
    Jan 2005
    Posts
    15362

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by OlfCNC View Post
    You can use the debounce filter of the UCCNC to filter out noise on your limit switch inputs.
    You can set a few milliseconds and then those short noise spikes will be ignored by the controller.
    Band-aids are not a way to fix something like this
    Mactec54

  10. #10
    Join Date
    Jun 2015
    Posts
    943

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by mactec54 View Post
    Band-aids are not a way to fix something like this
    It is done like that in the industry. You cannot always get rid of all the noise in industrial environments.

  11. #11
    Join Date
    Jan 2005
    Posts
    15362

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by OlfCNC View Post
    It is done like that in the industry. You cannot always get rid of all the noise in industrial environments.
    Yes you can if you know what you are doing Hobby or Industrial makes no difference
    Mactec54

  12. #12
    Join Date
    Jun 2015
    Posts
    943

    Re: Does wiring for limit switches need to be shielded?

    Hobby and industrial actually makes a huge difference. In a hobby environment you usually working in a garage with not many powerful machinery working around your little hobby machine.
    In industrial environments there are usually welding machines, plasmacutters, large lathes and mills switching tens and hundreds of ampers around causing lots of EMI.
    Which can cause noise issues to your little hobby machine in that noisy industrial environment.

  13. #13
    Join Date
    Jan 2005
    Posts
    15362

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by OlfCNC View Post
    Hobby and industrial actually makes a huge difference. In a hobby environment you usually working in a garage with not many powerful machinery working around your little hobby machine.
    In industrial environments there are usually welding machines, plasmacutters, large lathes and mills switching tens and hundreds of ampers around causing lots of EMI.
    Which can cause noise issues to your little hobby machine in that noisy industrial environment.
    You live in a country that has EMI noise restrictions and all industries have to be compliant required by code, there should not be any difference in both environments if there is then you are not code compliant

    Just learn how to wire your machines so there is no interference that can change the way it runs it's very easy to do, even in the industry with any amount of amps being switched should not affect any other machine on the same Mains supply, Noise is easy to fix if you know how and what to look for
    Mactec54

  14. #14
    Join Date
    Jun 2015
    Posts
    943

    Re: Does wiring for limit switches need to be shielded?

    Seems to me that you have never worked in the industry. I live in Sweden where everything is regulated but noise does not care about the regulations.

  15. #15
    Join Date
    Sep 2019
    Posts
    197

    Re: Does wiring for limit switches need to be shielded?

    I agree with what mac said...a filter is important, it will not filter out everything but it is something you will need anyway. There are lots of other things that could be causing your issues. A pic of your layout/wiring would help

  16. #16
    Join Date
    Jan 2005
    Posts
    15362

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by OlfCNC View Post
    Seems to me that you have never worked in the industry. I live in Sweden where everything is regulated but noise does not care about the regulations.
    You don't have a EMI noise problem if the whole electrical system is compliant that is what the regulations are for in your country which I already said

    As for not working in the industry have been in the industry my whole life, I have my own Industrial machine shop as well, and other industrial property that I own in more than one country, even my Home workshop is up to industrial standards on a smaller scale which has Machining centers Mills and Lathes Surface Grinder Injection molding and fabrication and all types of welding I never have a noise problem on my 400Amp residential Home Power supply

    An unusual snow fall we had showing part of my Homes 1.5 acres

    Just some snips of my Home shop there is much more but I'm not one to brag enjoy
    Mactec54

  17. #17
    Join Date
    Jun 2015
    Posts
    943

    Re: Does wiring for limit switches need to be shielded?

    The issue is that even in a country where everything like EMI emission is regulated people often do not care.
    You just start using a cheap chinese welding or plasma equipment and you can get noise issues.
    Like in this case the OP started using a chinese VFD and he is having noise problems.
    A quick fix could be to use the debounce filter in the UCCNC, but ofcourse filtering the noise is the best solution, just sometimes it is not easy.

  18. #18
    Join Date
    Jan 2005
    Posts
    15362

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by OlfCNC View Post
    The issue is that even in a country where everything like EMI emission is regulated people often do not care.
    You just start using a cheap chinese welding or plasma equipment and you can get noise issues.
    Like in this case the OP started using a chinese VFD and he is having noise problems.
    A quick fix could be to use the debounce filter in the UCCNC, but ofcourse filtering the noise is the best solution, just sometimes it is not easy.
    Using debounce has trade off and is just a band-aids for a real problem it does not matter what equipment you use or where it is from cheap or expensive correct wiring practices solve all these problems
    Mactec54

  19. #19
    Join Date
    Jun 2013
    Posts
    454

    Re: Does wiring for limit switches need to be shielded?

    Quote Originally Posted by OlfCNC View Post
    You can use the debounce filter of the UCCNC to filter out noise on your limit switch inputs.
    You can set a few milliseconds and then those short noise spikes will be ignored by the controller.
    Hey Olf thank you for the suggestion, Ill have to pencil that down and find out where it is in the menus.

    Cheers,
    Steve

  20. #20
    Join Date
    Jun 2013
    Posts
    454

    Re: Does wiring for limit switches need to be shielded?

    Cheers for that mate,

    Not to expensive to buy and having one won't hurt.

    Cheers,
    Steve

Page 1 of 2 12

Similar Threads

  1. Does limit switch wiring have to be shielded
    By ozydel in forum Benchtop Machines
    Replies: 8
    Last Post: 01-02-2015, 06:22 AM
  2. wiring limit switches
    By billsnogo in forum Bridgeport / Hardinge Mills
    Replies: 0
    Last Post: 11-18-2014, 12:42 AM
  3. Shielded wire for home/limit switches on g540
    By 990x in forum Gecko Drives
    Replies: 15
    Last Post: 01-19-2013, 11:35 PM
  4. Series Limit Switches with Shielded Wire
    By Wolfspaw in forum DIY CNC Router Table Machines
    Replies: 2
    Last Post: 12-27-2011, 09:54 PM