585,954 active members*
4,283 visitors online*
Results 1 to 18 of 18
    Jul 2019
    23
    Is this Relay-VFD wiring correct?
    Nearly finished upgrading my 6040Z with 12V PSU and Parallel BOB (TX14692) to 24V and USB BOB (BSMCEO4U-PP), just not sure what wires from the VFD to connect the NO/COM/NC side of the relay.
    Do VFD COM/FWD pins normally take 24V control signals? And is the relay supposed to short the ACM/Common to NO/FWD?
    Something about this doesn't seem right.
    I feel like it should be the +10V, but that's used for analog speed control right, so surely it shouldn't go through the relay?
    (which, btw, do you always connect +10V from the VFD to the BOB? Or only if 10V rails aren't already provided by the BOB?)
    I originally thought AVI and ACM were the analog signals, but there's no ACM on the VFD, so now I'm confused. Nothing else I've read so far has made it clear or actually shown a schematic for the relay to a VFD like this one.
    15362
    Re: Is this Relay-VFD wiring correct?
    Quote Originally Posted by Tophness View Post
    Most of these VFD drives for FWD there is no voltage needed the way you have it wired is incorrect from the relay output this should be direct to the VFD FWD and DCM Terminals
    +10 volts is only normally used if you don't have a PWM to 0-10v Analog output
    You will fry the VFD Drive input if you add any voltage to them
    Mactec54
    Jul 2019
    23
    Ah ok thanks. There's no DCM on this VFD though. Did you just mean COM? Or connect it to the DCM on the BOB?
    And I still connect both AVI together right?
    But not referenced to the ACM on the BOB? I would have thought that would make it floating, but in every other schematic I've seen there are separate grounds for DCM and ACM on the VFD, so I'm not sure if I should wire the BOB's ACM to VFD's COM.
    15362
    On some VFD Drives Com is the same as DCM Take some close up photos of the VFD Drive terminals so I can see what you have
    Mactec54
    Jul 2019
    23
    That cap underneath reads "7uF25V 47uF", but I'm not sure if it's even connected to +10V/COM/FWD
    15362
    That is correct Yellow and Black wire to the Relay, I need to see the Breakout board inputs / output as well for the 0-10v output
    Don't worry about the 10v terminal this is mostly not used
    Mactec54
    Jul 2019
    23
    Ahh I see, so you're just shorting the VFD's FWD pin to it's own ground?
    15362
    Correct no voltage needed, why did you need the Rely as your Breakout Board can connect direct
    All you need to use for your speed control is AVI on your Breakout Board and Ground to connect to the VFD Drive AVI and Com then there will be 1 or 2 Parameters to set in the VFD Drive for that to work,
    Why did you need the Relays, you can connect output 1 to FWD on the VFD Drive, that should work also without the Relays
    Mactec54
    Jul 2019
    23
    From what I understand this BOB has 24V outputs. The relay takes 24V control signals, and other setups I've seen used relays for it (https://www.youtube.com/watch?v=Qi4M3DAtTXg).
    I didn't want to fry the VFD input pins with too much voltage. I've tested the relay by itself with nothing connected and 24V activates it so that must be right.
    So I do connect the ACM on the BOB to VFD COM? Or is it some other ground? Surely ACM would be a better reference for analog voltage than the 5v/10v/24v ground?
    And does that mean the VFD has a shared analog/digital common? Cos I haven't seen any schematics using it like that yet
    15362
    Stop looking at misguided information
    Your Relays Output does not Output any Voltage unless you add it, this is just a switch On / Off nothing more there is no voltage involved between the VFD Drive FWD connection and the Relay if there is you have it wired wrong
    The only other voltage involved is the 0-10v Analog output ( AVI which you need to check at the Board ) from your Breakout Board so there is no 24v involved in the connection between the VFD and your Breakout Board
    24v can be used from Output 1 if the VFD Drive is setup correctly it would have to be changed from NPN to PNP but I'm not sure you would be able to do that unless there is a switch / Jumper on the Board for that
    Some VFD Drives ACM and DCM is the same connection also called ( COM ) ACM if your VFD had it would be the correct choice for the Analog connection
    Mactec54
    Jul 2019
    23
    Ahh ok I think I understand now. I guess I'll just use the relay anyway rather than risk getting that wrong, plus it's isolated so it should help with shielding.
    Just making sure, it should be wired like this right?
    VFD AVI >>> BOB AVI
    VFD COM >>> BOB GND + Relay COM
    VFD FWD >>> Relay NO
    15362
    VFD AVI >>> BOB AVI
    Correct this should work fine But check that the AVI is working correctly before you connect it to the VFD Drive needs to be 0-10v so you can do in MDI M3S12000 and you should get around 5v if you have setup Mach3 Correct
    Mactec54
    Jul 2019
    23
    No luck. I tried every port from pins 0-4. Between AVI and GND I always get 0V.
    Between the BOB's 24V rail and FWD output I get 24V when it's active and 0V when it's not, and strangely if I set the spindle motor outputs to that port, between 24V and OUT1 (spindle) I get 5V.
    Maybe I could use that to PWM it instead of AVI, but it was supposed to have a dedicated 0-10V analog output.
    Also, between GND and 10V, I get 0V. Maybe the 10V pin is supposed to be an input from the VFD's 10V rail, not an output, and it just shapes it and outputs it to AVI.
    15362
    You can not use PWM
    Your Breakout Board may be bad or you have not setup Mach3 ports and pins correct
    You have to get your Breakout Board working correct before you can connect anything to the VFD
    Mactec54
    Jul 2019
    23
    With nothing left to try, I measured 10V on the VFD's +10V output rails and connected it to the BOB's 10V, since online documentation said it was different on this board and it was an input instead of output.
    This seemed to be correct, since I measured ~9.65V between the BOB's GND and AVI.
    That was doing M3S12000 though. So what now? Is that twice the voltage it should be? Will it go higher on other settings? I still haven't connected the BOB's AVI and spindle AVI together yet, cos I don't want to risk overvolting the VFD.
    15362
    Yes that is correct some Breakout Boards need a 10v or higher supply for the AVI to work, we don't have your Breakout Board spec's to know what it needs
    It is obvious that it is not being controlled being 9.65v would be close to max so while it has an output, to see if it is working you have to do your own trying at different speeds to see if it is changing if it is not then you have a setup problem in the control
    12,000 is just a test you need to try other speeds and see if it is doing anything
    Mactec54
    Jul 2019
    23
    All working now. S24000 took it up to 9.9V so I went ahead and connected it.
    Thanks for the help. Crazy that the documentation says 10V input but all the user-provided and seller-provided schematics show the 10V rail not even connected on this BOB as if it had it's own 10V regulator or something.
    15362
    The 10v is not always needed as most Breakout Boards complete that part of the VI 0-10v analog output within the Breakout Board, quite often this is changed by a jumper or a switch
    Normally when this is obvious there are 3 connections on the same Terminal block +Vin / Aout / G or 10v+ / VI / Ground
    Mactec54
  1. E-stop wiring, which way is correct?
    By secretspy in forum CNC Machine Related Electronics
    Last Post: 09-14-2018, 11:27 PM
  2. is this wiring correct? + have 2 questions...
    By effimos in forum DIY CNC Router Table Machines
    Last Post: 03-31-2012, 12:32 AM
  3. Wiring Aux 1 relay
    By SWATH in forum Mikinimech
    Last Post: 02-29-2012, 07:26 PM
  4. Correct voltage and amp. on m-code relay
    By kbspeed in forum Haas Mills
    Last Post: 10-12-2010, 09:14 PM
  5. Correct Relay board for Mach and router
    By WilliamD in forum Mach Software (ArtSoft software)
    Last Post: 04-17-2008, 12:54 AM
