    Is my transform wired correctly?

    Sorry to ask such a simple question but I'm trying to cover all my basis. I have a new to me CNC mill with unknown history. It has a transformer that needs to be wired based on input voltage. It was setup for 208 single, and mine is coming in at 249. I'm asking this cause I'm getting some weird voltage readings throughout the cabinet where I feel I should be getting 120. The following diagram is how I have it wired and what the output voltages are. Why is the reading from E-OV 99? shouldn't it be 0? I'm seeing these half voltages throughout the cabinet. Funny thing is most of the machine is working. I'm trouble shooting a spindle issues and I need to take this transformer off the list.


    Thanks.




















  2. #2
    Join Date
    Aug 2009
    Posts
    1573

    Re: Is my transform wired correctly?

    ...What about the Interconnects..can't see them in the photo. 208v input would have had a H4 to H10 jumper..Did you remove it..?

  3. #3
    Join Date
    Nov 2006
    Posts
    33

    Re: Is my transform wired correctly?

    There is two jumpers both the dark and light green in the first photo.

  4. #4
    Join Date
    Nov 2006
    Posts
    33

    Re: Is my transform wired correctly?

    Ohh the actual wires have been removed and replaced with drawn, so its easier to see.

  5. #5
    Join Date
    Aug 2009
    Posts
    1573

    Re: Is my transform wired correctly?

    Quote Originally Posted by funford View Post
    There is two jumpers both the dark and light green in the first photo.
    ...your drawing looks correct for 240v.

  6. #6
    Join Date
    Nov 2006
    Posts
    33

    Re: Is my transform wired correctly?

    Are the output measurements correct? Is E to Ov suppose to have voltage? I thought ov was neutral and e was earth ground. But have know idea if a transformer like this is suppose to read such.

  7. #7
    Join Date
    Dec 2013
    Posts
    5717

    Re: Is my transform wired correctly?

    If you are measuring from the terminal to earth ground (E) or cabinet ground, you may get some erroneous readings. You need to measure leg to leg. The leg to leg output voltages are what I would expect, 42 and 122
    Jim Dawson
    Sandy, Oregon, USA

Similar Threads

  1. How can transform G02/G03 to G01... help !
    By costy35 in forum Uncategorised CAM Discussion
    Replies: 4
    Last Post: 02-14-2015, 04:51 PM
  2. SolidCam; Transform; How to transform operations for individual parts
    By Binze in forum SolidCAM for SolidWorks and SolidCAM for Inventor
    Replies: 12
    Last Post: 11-05-2014, 11:22 AM
  3. More transform help
    By orion_134 in forum Mastercam
    Replies: 3
    Last Post: 01-20-2014, 01:02 PM
  4. Are my motor windings wired correctly?
    By ceefna in forum Phase Converters
    Replies: 16
    Last Post: 03-23-2012, 12:30 AM
  5. Are my encoders wired correctly?
    By RP Designs in forum Servo Motors / Drives
    Replies: 8
    Last Post: 10-20-2009, 01:14 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •