    reinitialization of mitsubishi M3 control

    It seems battery issues force me to reinitialize the control.
    Getting Buss error on some screens.

    So i have most of the backups done:

    From page 1 on screen
    #1 programs (including tool change program)
    #2 Tool data
    #3 Parameters
    #5 Common variables

    from page 2 on screen
    I was not able to get:
    #30 Macro programs
    #40 robot programs (we do not use a robot)
    #50 Basic
    #60 trace data

    I did get from page 2
    #99 all 1 (execpt 102 axis independent parameter
    #99 all 2
    #99 all 3

    I also have all the original parameters from manufacture. (it is a Dyna mechatronics DM4800)

    Do i have enough backups to reinitialize this control.
    Any hints would be helpful.

    Concerned about the plc data being lost.
    I have the procedure to reinitialize from Mitsubishi.
    Thanks
    Mike

  2. #2
    Join Date
    Nov 2012
    Posts
    363

    Re: reinitialization of mitsubishi M3 control

    PLC data, I'm almost certain, is in EPROM, so you should be fine there.