    Daewoo puma 8s Fanuc OTC parameters need HELP

    hi please help need parameters for lathe Daewoo Puma 8s 1995 year Fanuc OTC turret 10 tools
    please helps

  2. #2

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    i receive parameters and pmc parameters for similar machine 8s i reload but still have problem machine not works
    when i turn on machine shows
    PLC loading data
    1 load from IO
    3 run
    4 run without pmc
    i put run but shows LADDER NOT EXIST any IDEA???

  3. #3

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    On that controller the ladder is typically burned on EPROM's. However, you could have a development board that is used till the ladder has been proven out then you burn the ladder to EPROM's. Looks like they didn't do that so now you don't have a ladder. Can you post a pic of the controller? You probably have PMC-M which means that the EPROM's would be on that board. If you have PMC-L then the EPROM's would be located on the Memory board marked 0E1 & 0E2. The other possibility is that your machine has the ladder PMC type set incorrectly. Post the parameters as well. Verify that the backup file that you used for the parameters contain the 900's parameters. These are NOT saved if whoever did the saving didn't press and hold EOB when saving them.

  4. #4

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    [IMG]www.zapodaj.net/2a842194a341d.jpg.html[/IMG]
    [IMG]www.zapodaj.net/60f5d316bf06c.jpg.html[/IMG]
    [IMG]www.zapodaj.net/b74888758ec0b.jpg.html[/IMG]

    i have parameter from similar machine,i load everything from similar machine and if i try press 3 run show ladder not exist i dont know how to resolve this :/
    i try change 905 parameter also bit by bit and nothing,this parameter read PMC


    N0900 P 00111000
    N0901 P 11100001
    N0902 P 00000100
    N0903 P 10001000
    N0904 P 00000000
    N0905 P 00000001
    N0906 P 00100000
    N0907 P 01010000
    N0908 P 00000000
    N0909 P 00100001
    N0910 P 00000000
    N0911 P 00000000
    N0912 P 00000000
    N0913 P 00000000
    N0914 P 00000000
    N0915 P 00000000
    N0916 P 00000000
    N0917 P 00000010
    N0918 P 00000000
    N0919 P 00000000
    N0920 P 00000000
    N0921 P 00000000
    N0922 P 00000000
    N0923 P 00000000
    N0924 P 00000000
    N0925 P 00000000
    N0926 P 00000000
    couple my parameters 900

  5. #5

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Looks like you have PMC-L which means you have to have EPROMs on the Memory board at 0E1 & 0E2. Your pics didn't come through

  6. #6

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Quote Originally Posted by drdos View Post
    Looks like you have PMC-L which means you have to have EPROMs on the Memory board at 0E1 & 0E2. Your pics didn't come through
    yes THERE IS 2 EPROMS oe1 AND oe2 but looke like not read this eproms

  7. #7

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Click image for larger version. 

Name:	IMG-1927 (1).jpg 
Views:	2 
Size:	87.2 KB 
ID:	456913
    Click image for larger version. 

Name:	IMG-1928 (1).jpg 
Views:	2 
Size:	92.5 KB 
ID:	456915
    Click image for larger version. 

Name:	IMG-1929 (1).jpg 
Views:	1 
Size:	93.3 KB 
ID:	456917

  8. #8

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    These attachments are not working either. Do you have a backup of the ladder? Most people don't. May have to see if Daewoo can provide.

  9. #9

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Doosan said cant help machine is too old

  10. #10
    Join Date
    Oct 2009
    Posts
    297

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Quote Originally Posted by wojtekthx View Post
    Doosan said cant help machine is too old
    Hello:
    Try replacing the memory board. Replace all the chips that can be replaced.
    If you still have the same problem, you could have a bad EPROM. (Either OE1 or OE2 or both)
    Do you know if you have the ladder in paper?

    Regards

    AlexFanuc

  11. #11

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    machine works i change 2 eproms for another and change mem card for another
    now read pmc and show ladder
    axis works,spindle works but i have probelm with turret maybe that why becouse input parameters from lathe puma 8s wiTH 12 turret tools i have 10 on own machine turret tools
    i find in on web diagnostic D443 parameter on my machne is all 00000000
    help how change this
    error on Daewoo display is 27 number something with time exceeded changing tools(key works i check in diagnostic )turret not index any tools ,valves solenoid on turret led is off there is 2 valves and 4 position, both not shine like pmc not control this valves
    Attachment 457358

  12. #12
    Join Date
    Oct 2009
    Posts
    297

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Quote Originally Posted by wojtekthx View Post
    machine works i change 2 eproms for another and change mem card for another
    now read pmc and show ladder
    axis works,spindle works but i have probelm with turret maybe that why becouse input parameters from lathe puma 8s wiTH 12 turret tools i have 10 on own machine turret tools
    i find in on web diagnostic D443 parameter on my machne is all 00000000
    help how change this
    error on Daewoo display is 27 number something with time exceeded changing tools(key works i check in diagnostic )turret not index any tools ,valves solenoid on turret led is off there is 2 valves and 4 position, both not shine like pmc not control this valves
    Attachment 457358
    Hello:
    PWE= 1
    MDI MODE
    PROGRAM EDIT KEY OFF
    CHANGE PARAMETER

    Regards
    AlexFanuc

  13. #13

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    ok let you know tommorow

  14. #14

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Quote Originally Posted by wojtekthx View Post
    ok let you know tommorow
    yes thats works with this procedure diagnostic,i change diagnostic parameter

    but system wont index turret but no power on relays and valves solenoid
    Click image for larger version. 

Name:	D51C161E-A18F-410B-910F-9051CE072E6B (1).jpg 
Views:	0 
Size:	115.8 KB 
ID:	457374
    Click image for larger version. 

Name:	DD5750AF-F828-44A9-8138-7690F7AD2E54.jpg 
Views:	0 
Size:	120.4 KB 
ID:	457376

  15. #15

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Click image for larger version. 

Name:	IMG-1984.jpg 
Views:	3 
Size:	107.2 KB 
ID:	457378

  16. #16
    Join Date
    Oct 2009
    Posts
    297

    Re: Daewoo puma 8s Fanuc OTC parameters need HELP

    Quote Originally Posted by wojtekthx View Post
    Click image for larger version. 

Name:	IMG-1984.jpg 
Views:	3 
Size:	107.2 KB 
ID:	457378
    Hello:

    Ask for tool number 1
    Before you (cycle) take a look at the ladder Y49.4
    Is it turning on?

    Regards

    AlexFanuc

Similar Threads

  1. Replies: 2
    Last Post: 05-07-2023, 02:06 AM
  2. Parameters Backup - Daewoo puma 160 lathe - Fanuc 0i TA
    By juliosantos in forum Daewoo/Doosan
    Replies: 7
    Last Post: 09-16-2019, 03:21 PM
  3. Daewoo Puma 250B parameters
    By bluej_x in forum Daewoo/Doosan
    Replies: 6
    Last Post: 11-06-2013, 09:15 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •