    I have a NEMA34 plug 'n' play electronics system, and am using Mach4. I just bought a Huanyang HY VFD - everything is working great except the 0-10V signal doesn't get to 10V when connected to the VFD.

    If I unplug the 0-10V wires from the VFD, the wires measure 0V at minimum speed command, and 10V at max speed - just as I would expect.

    However, when I plug it into the VFD, when I command full speed in Mach4 (24000RPM), the terminals only measure about 8V, and the spindle only gets to about 20,400 RPM.

    I have contacted AVID support, so I'll see what they say --- has anyone encountered this issue and been able to fix it themselves? Thanks.

    I found a similar thread to this issue - it's not clear to me if a new board fixed it or different settings.

    https://www.cnczone.com/forums/avid-...mp-play-2.html

  2. #2
    Join Date
    Mar 2003
    Posts
    35538

    Re: 0-10V Signal Not working w/ HY VFD

    Not sure what speed control AVID uses, but most speed controls have a small voltage drop at max voltage, but it's usually a little over 9V.
    Most VFD's have settings to compensate, but the HY does not.

    Hopefully AVID has a solution.

    What I did (using UCCNC) was to set the max PWM in the software to 50% and set the Huanyang to 0-5V, and it worked well.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  3. #3

    Re: 0-10V Signal Not working w/ HY VFD

    Yea unfortunately the HY is a fixed 0-10V. If I could adjust the 10V down to 8V, this would be easily solved.

  4. #4
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by Wood768dGuy View Post
    Yea unfortunately the HY is a fixed 0-10V. If I could adjust the 10V down to 8V, this would be easily solved.
    What is the wire / cable you are using to connect it to the VFD Drive it may not be suitable

    If it is a genuine Huanyang then it has both 0-10v or 0-5v option
    Mactec54

  5. #5

    Re: 0-10V Signal Not working w/ HY VFD

    The cable is suitable - it's AVID's OEM cable. It's 20AWG wire. This is not a voltage drop due to wire resistance. I'm not sure anyone could buy a cable with wire small enough to have that be the issue - I could be using ethernet cable w/ 26AWG wire and it would be sufficient.

    My next step is to move two wires inside the AVID control box, and switch to PWM signal that their breakout board outputs.

  6. #6
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by Wood768dGuy View Post
    The cable is suitable - it's AVID's OEM cable. It's 20AWG wire. This is not a voltage drop due to wire resistance. I'm not sure anyone could buy a cable with wire small enough to have that be the issue - I could be using ethernet cable w/ 26AWG wire and it would be sufficient.

    My next step is to move two wires inside the AVID control box, and switch to PWM signal that their breakout board outputs.
    You would be surprised what wire some people use I have seen 10Gauge Romex solid core wire used so one has to ask

    You can only use the PWM signal if you have a Digital to Analog converter to give you the 0-5v or 0-10v analog, output You can not connect the PWM signal direct to the VFD Drive you have

    A PWM output is not normally used for VFD Drive control, you can use a regular spare output with a converter
    Mactec54

  7. #7
    Join Date
    Mar 2003
    Posts
    35538

    Re: 0-10V Signal Not working w/ HY VFD

    Didn't realize you could adjust that with those settings. Funny that the manual says 0-400, but it allows 459.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  8. #8

    Re: 0-10V Signal Not working w/ HY VFD

    Yea I got lucky there - I had the exact same thought. I tried to program 401 Hz into PD072 before I went thru the trouble of doing this analysis...was pleasantly surprised it worked!

  9. #9
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by Wood768dGuy View Post
    Yea I got lucky there - I had the exact same thought. I tried to program 401 Hz into PD072 before I went thru the trouble of doing this analysis...was pleasantly surprised it worked!
    Yes this means you are pushing higher Frequency into the spindle for the low voltage compensation not ideal as the spindle is only rated for 400Hz but if it lasts ok and works go for it

    Some use pulley ratio adjustment in there control software and the PWM Frequency to adjust for the spindle speeds
    Mactec54

  10. #10

    Re: 0-10V Signal Not working w/ HY VFD

    The VFD is programmed to 400 Hz max. PD005 = 400 sets the max frequency the VFD will output. The VFD never drives higher than 400 Hz.

    PD072 and PD073 program the curve the selected signal (in my case 0-10V, PD070=0) the VFD uses to calculate desired output frequency from the 0-10V signal. If that calculation yields a value higher than 400Hz, the VFD will only output 400 Hz.



    On your note about PWM frequency - I don't see how that would varying PWM frequency would have any affect on anything, since PWM, by definition, has a fixed frequency. If it's a variable frequency signal, then it is not a PWM signal.

  11. #11
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by Wood768dGuy View Post
    The VFD is programmed to 400 Hz max. PD005 = 400 sets the max frequency the VFD will output. The VFD never drives higher than 400 Hz.

    PD072 and PD073 program the curve the selected signal (in my case 0-10V, PD070=0) the VFD uses to calculate desired output frequency from the 0-10V signal. If that calculation yields a value higher than 400Hz, the VFD will only output 400 Hz.



    On your note about PWM frequency - I don't see how that would varying PWM frequency would have any affect on anything, since PWM, by definition, has a fixed frequency. If it's a variable frequency signal, then it is not a PWM signal.
    In your control you can change the PWM output to what ever you want, unless you control has it fixed which I doubt that they have done that

    The PWM depending on the Breakout Board converter changing this can change the voltage output on most boards 100 is normally 10v 50 is 5v you can usually change this number to get your 10v output or 5v which ever you want to use

    Without measuring the frequency you don't really know what it is doing

    PD072
    PD073
    Are both spindle speed control changing either numbers will change the spindle speed regardless of the PD070 voltage

    I'm not sure how this will affect the VFD Drive component's in the long term, time will tell I'm sure the components have some over rating before they fail
    Mactec54

  12. #12

    Re: 0-10V Signal Not working w/ HY VFD

    The output I am using on my BoB is 0-10VDC. It is not a PWM signal. My breakout board offers only 0-5V PWM and 0-10VDC.

    I can see on the frequency display on the VFD that it never commands the above 400 HZ. I also have a photo tach that reads speed is not exceeding 24,000 RPM.

    The VFD drive components are not seeing anything out of the norm b/c the voltage from my BoB to the VFD is only 0-8VDC - which is the problem I had that started this whole thread.

    Quote Originally Posted by mactec54 View Post
    You can only use the PWM signal if you have a Digital to Analog converter to give you the 0-5v or 0-10v analog, output You can not connect the PWM signal direct to the VFD Drive you have
    Lastly - this comment here regarding the need for a converter is flatly wrong. I connected the 0-5V PWM from my BoB directly to ACM/VI terminals on the VFD, set PD070=0 (configures input for 0-5V) and everything works perfectly fine.

    For posterity should anyone stumble upon this later, this was my final solution -

    PD070=1 (0-5V)
    PD072=400 (Higher frequency. i.e. 5V = 400Hz)
    PD073=100 (Lower frequency. i.e. 0V = 100 Hz)

    Default freq. of the PWM signal by default from AVID/Warp9 is 2kHz.

  13. #13
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by Wood768dGuy View Post
    See this statement here: Sounds a lot like you think I'm pushing a frequency higher than the rated 400Hz.
    You where: to compensate for the low voltage instead of fixing the real problem, that is what you posted you where doing


    Quote Originally Posted by Wood768dGuy View Post
    Respectfully disagree, found several other threads where others have fed a 0-5V PWM into the 0-5V input - lots of Shapeoko users, etc. This is ultimately what lead me to try it despite the fact you said it wouldn't work. The place people run into issues is if the frequency of the PWM is too low - I tested and the speed is rather unstable < 1000 Hz.
    Not everyone has a Smooth Stepper where you can crank up the PWM Frequency to try and make it look like an analog signal

    How long will it last with that High frequency being used the High Frequency PWM will make it look like it is similar to an analog signal only time will tell as to how long the VFD Drive will handle's this before it fails

    You need to put a scope on it to see how nasty it is, and put a low pass filter on it, hats off to the manufacture if it survives it means they have compensated for it and made there VFD Drive immune to multiple options

    Quote Originally Posted by Wood768dGuy View Post
    I have an AVID CNC, which I stated in my initial post - it ships with an Ethernet Smoothstepper and pre-configured from AVID to be set up correctly to control a spindle. I did review thoroughly the settings and they are set up correctly.
    But you can adjust Parameters from what the setup Parameters are to get the outputs you require

    You are not the first one to have this problem with there Breakout Board, they have changed there Breakout Board for some of there customers to solve this problem


    As for this post
    Quote Originally Posted by mactec54
    Yes this means you are pushing higher Frequency into the spindle for the low voltage compensation not ideal as the spindle is only rated for 400Hz but if it lasts ok and works go for it

    Yes I could of worded that post a little better, just one word incorrect it should of been VFD Drive it is obvious by the post that it is related to the low voltage compensation which can only be changed by the VFD Drive, or in the control
    Mactec54

  14. #14
    Join Date
    Mar 2003
    Posts
    35538

    Re: 0-10V Signal Not working w/ HY VFD

    You where: to compensate for the low voltage instead of fixing the real problem, that is what you posted you where doing
    No, not if you read what he wrote.
    He would have IF he was providing 10V, but he wasn't. He adjusted the VFD to get 400Hz at less than 10V.
    Gerry

    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html

    Mach3 2010 Screenset
    http://www.thecncwoodworker.com/2010.html

    JointCAM - CNC Dovetails & Box Joints
    http://www.g-forcecnc.com/jointcam.html

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  15. #15
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by ger21 View Post
    No, not if you read what he wrote.
    He would have IF he was providing 10V, but he wasn't. He adjusted the VFD to get 400Hz at less than 10V.
    I think there is a misunderstanding adding 459Hz to PD072 was to increase the frequency to compensate for the low voltage nothing more to it
    Mactec54

  16. #16

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by mactec54 View Post
    You where: to compensate for the low voltage instead of fixing the real problem, that is what you posted you where doing
    No I wasn't. PD005=400 places a hard upper limit on the frequency output at 400HZ. While the VFD may have calculated a frequency greater than 400HZ based on the control voltage, it would never actually output something higher than 400HZ. Under no circumstance would the VFD output more than 400HZ.

    Quote Originally Posted by mactec54 View Post
    How long will it last with that High frequency being used the High Frequency PWM will make it look like it is similar to an analog signal only time will tell as to how long the VFD Drive will handle's this before it fails

    You need to put a scope on it to see how nasty it is, and put a low pass filter on it, hats off to the manufacture if it survives it means they have compensated for it and made there VFD Drive immune to multiple options
    I stand by my earlier comment regarding certitude vs. accuracy.

    Why anyone would do this on a $100 VFD when there are a great number of folks that have had it wired this way for years with success is beyond me. This is a solution in search of a problem.

  17. #17
    Join Date
    Jan 2005
    Posts
    15362

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by Wood768dGuy View Post
    No I wasn't. PD005=400 places a hard upper limit on the frequency output at 400HZ. While the VFD may have calculated a frequency greater than 400HZ based on the control voltage, it would never actually output something higher than 400HZ. Under no circumstance would the VFD output more than 400HZ.
    You have no clue what or how your VFD Drive works

    PD072 has noting to do with PD005=400 you did a Graph to show us that you could use PD072 to compensate for the low voltage, I guess it did not work out for you or you would be still using it, Pos # 7 says what you hoped would work


    Quote Originally Posted by Wood768dGuy View Post
    Why anyone would do this on a $100 VFD when there are a great number of folks that have had it wired this way for years with success is beyond me. This is a solution in search of a problem.
    That is totally false information you are the first here on the Zone to post with a Huanyang that you are using a PWM signal to control the speed on this VFD Drive, there is no one here been doing this for years most who have tried failed

    The only reason you can use it is because of the high frequency output you have, all it is doing it is trying to fool the drive into thinking it is an analog signal
    Mactec54

  18. #18

    Re: 0-10V Signal Not working w/ HY VFD

    Quote Originally Posted by mactec54 View Post
    You have no clue what or how your VFD Drive works
    Noted, thank you. It's odd that it's functioning exactly like I want it to, I guess ignorance is bliss.

    Quote Originally Posted by mactec54 View Post
    PD072 has noting to do with PD005=400 you did a Graph to show us that you could use PD072 to compensate for the low voltage, I guess it did not work out for you or you would be still using it, Pos # 7 says what you hoped would work
    What I described in post #7 did work, I tested and verified - linear regression isn't rocket science. I like to tinker and wanted to see if the PWM would work since I read that many Shapeoko owners over in the Carbide3D forums use the PWM from the Shapeoko controller (7.8kHz 0-5V PWM) with the Huanyang HY model. I learned along the way that the VFD can indeed accept a PWM on the 0-5V input, and that it works best on frequencies above 1kHz. My hope is this post is insightful to someone in the future.



    PD005, PD011, PD072, and PD073 can be related. See the attached chart I created to illustrate. For instance, even if PD072 is set greater than PD005, the output frequency is clipped to PD005.

Similar Threads

  1. Replies: 3
    Last Post: 06-08-2019, 11:59 PM
  2. Replies: 1
    Last Post: 05-19-2019, 12:26 AM
  3. Replies: 0
    Last Post: 11-14-2017, 11:14 PM
  4. Replies: 15
    Last Post: 11-10-2014, 03:29 PM
  5. Step signal not working
    By jrsaw27 in forum Mach Mill
    Replies: 19
    Last Post: 02-28-2013, 12:04 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •