Good morning,
i just had a problem with the control of the fanuc 6M and I have to transfer the macros to the control.
So that there is a procedure but not the memory ... can someone help me?
infinitely thank you
Good morning,
i just had a problem with the control of the fanuc 6M and I have to transfer the macros to the control.
So that there is a procedure but not the memory ... can someone help me?
infinitely thank you
You have the Macros?
There is a Macro Screen on the 6M ?
Can you output them at all what is in there ?
ay o hey hows it going
6t here random question for you guys about the program directory relating to 071 error
Error 71 ----------------The Address to be searched for was not found ---------------means the program or macro address is not there
so i had an issue where an operator went about fixing this error and wiped programs that were in the machine since we got it, now it wont let me put in more than two programs when we had at least 10 decent sized ones.
throws the 71 error even though program name is not taken in the machine
Lost programs or Parameters ?
There is Parameters related to memory size
There is an optional parameter i think increases the memory size thats why i ask
When your are the machines create 3 or four sub programs with almost nothing in it and see if the control can recognize them
M98 P8000
M98 P8001 and just put and M99 in the subs for return --Will show if its memory size or something else
Yes and just uses the RS232 port for communication
Optional Parameters are the 900s if i remeber right lol
That controller is a 6T ?---------Big difference from 6t to the O controls in parameter and settings -----Anyway you have a great time and yes been along time since i worked on them controls when new lol