    Hi there!
    Quick question: can I chain the fault output of mutlitple CS-D508 drivers like this?
    (details on p10 of this manual: http://leadshineusa.com/UploadFile/D...-D508_m3.1.pdf)
    Thx a lot!
    Dec 2013
    8
    Re: chain leadshine fault outputs?
    Please somebody! Maybe my schematic isn't clear enough?
    Nov 2012
    1267
    The manual does not explicitly say whether the alarm logic is positive or negative. If it is what I think it is, you can connect all ALM+ and ALM- outputs in parallel. An alarm in any driver(s) will pull the FAULT signal low.
    Jan 2018
    1516
    I can't see why not.
    Your attachment file doesn't work so I can't see how you wired it. So........
    If the ALM circuit is normally closed NC when drive is active and opens the circuit NO when a fault happens, then you would wire them in series.
    If the ALM circuit is normally open NO when drive is active and closes the circuit NC when a fault happens, then you would wire them in parallel.
    It says the ALM is configurable to a certain extent so this could possibly be adjustable.
    Manual suggests the alarm circuit sinks to ground.
    This circuit can then go to one of your controllers optocoupler inputs to trigger a stop.
    Or if your controller has lots of inputs, then you could just do them individually and assign each one.
    Or even use a multi channel optocoupler module between the two.
    Depending on your controller software you could assign one of the buttons such as stop or feed hold etc.