585,991 active members*
4,725 visitors online*
IndustryArena Forum > CNC Electronics > Spindles / VFD > AE200 VFD 10v analog control problem
Results 1 to 11 of 11
    Hello everyone,
    So i have a problem with controlling my VFD with mach3 BOB
    This is the BOB in question: https://www.vallder-rs.com/en/c/300/...s-board-detail
    This is the VFD in question: https://www.vallder-rs.com/en/c/436/...nverter-detail ( its 1.5kw one)
    Min spindle speed is 6000 and max 24000 rpm.
    I connected everything correctly and configured everything correctly i am sure of it.
    When i start the spindle at min speed it starts speeding up and stops at 6000 for a second and again starts speeding up to around 12000 and stops there.
    When i change speed in mach3 to 12000 ( through S12000 command) it starts slowing down for some reason.
    I think i found the problem but do not know how to solve it.
    To connect the mach3 BOB to VFD i use 3 VFD screw terminals called FV , GND COM and S1 respectively. S1 is used for starting the spindle and FV is used for +10V analog.
    The voltage between S1 and COM GND is 12.3V without anything connected. Voltage between FV and COM GND is 0V as it should be.
    I have 4 wires running from BOB to VFD : +10V , GND , relay COM , relay NO.
    the problem is that GND and relay COM have to go the same point of VFD ( GND COM);
    On BOB without connecting it to VFD 0-10V analog outputs correct voltage for all given S commands.
    When i start the spindle on 6000 relay activates and spindle starts speeding up the voltage somehow gets transfered over to FV from S1 and gets higher then it should be, to around 4V between FV and GND COM.
    The way to solve this is obviously to isolate GND from relay COM, but i do not know the way to do it.
    If this post is confusing i will record a video to demonstrate what is the problem.
    Thanks in advance for your responses.
    24221
    Re: AE200 VFD 10v analog control problem
    You do have it set for a 2pole motor I assume?
    If not, this could be the issue.
    Albert E.
    15362
    Quote Originally Posted by FrisscoCBR View Post
    Hello everyone,
    The Breakout Board needs 12v or more for the PWM 0-10v to be correct, the VFD Drive +10v is not enough
    If you are using Mach3 then you will may have to play with the Pulley Ratio 100Hz PWM setting is also a good starting number
    You need the Breakout Board 0-10v working correct before you connect it to the VFD Drive
    Do you have a PDF VFD Manual you can post
    Mactec54
    Nope, i have it set right actually. Thanks anyway.
    I have 12v 5A PSU powering BOB. I know about that. Breakout board is working perfectly before it is connected to the VFD. Every voltage is correct and outputs are working as expected.
    VFD manual is attached here.
    15362
    So what are you using the +10v for this should not be used anywhere, in your setup
    Your VFD Has Com and Ground connections they need to be used correctly
    FV -- Ground connection
    S1 -- Com connection
    Mactec54
    Jan 2018
    1516
    This is my take on it:
    If you're using voltage for speed control:
    It looks to me as though the voltage 0-10v goes into FV
    The ground goes into GND
    If you're using a PID frequency:
    It's FI & GND..... (pulse/direction?)
    The connection marked 10v looks to be an output to send power to a potentiometer for stand alone control of FI and GND.
    connect S1 to relay for M3
    connect S2 to nothing for M4
    Change 1 to low and 1 to high in Mach3. One of them will go on and one will go off when called for M3/M4. Depending on which direction you want to run, swap these over until it's correct.
    S1/S2 will be + voltage..... COM will be - voltage.
    That's how I would do it anyway but I can't guarantee this is all correct.
    15362
    Quote Originally Posted by dazp1976 View Post
    No guarantee what you posted is correct, confusion is a problem with posts like this
    PID has nothing to do with this type of control it is PWM to Analog 0-10v output nothing more to it
    Mactec54
    Jun 2013
    Hello,
    Did you solve the issue you have with this VFD?
    I bought the same from Vallder but I use a USB Mach3 controller instead of the one you use.
    However, I deal with a similar problem. VFD works ok through panel commands, however, I can't make it run through terminals. I can see frequency changing on the VDF screen, but the motor is not running. As far as I understand, it seems that start/stop is failing as there is no current on motor leads.
    Hvala.
    15362
    Quote Originally Posted by NikolajSim View Post
    Hello,
    Hvala.
    Do you have a relay, on an output, from your control, if so this would connect to S1 and com, this is just a switch no voltage required
    Mactec54
    Jun 2013
    Thanks for the hint! I have added a relay and changed output 1 to output 3 as this one is "on/off". Outputs 1 and 2 gave me PWM based on spindle speed so it couldn't activate a relay.
  1. Standalone USB to 0-10V analog control board?
    By cnczoner in forum CNC Machine Related Electronics
    Last Post: 12-06-2020, 01:39 AM
  2. RPI's 5v PWM to 0-10V analog for VFD
    By PropellerHat in forum OpenSource Software
    Last Post: 06-10-2020, 06:18 AM
  3. Huanyang VFD 10V Analog Signal Reversed
    By bleker in forum Spindles / VFD
    Last Post: 12-19-2016, 04:08 PM
  4. Replies: 3
    Last Post: 11-20-2014, 06:05 PM
  5. Analog +-10v to 0-5v conversion
    By epineh in forum CNC Machine Related Electronics
    Last Post: 06-01-2010, 04:21 AM