    Re: Need help ....Fuling Vfd, steel enclosure and small steps

    Quote Originally Posted by rjwims View Post
    Could you please give an an example of 1.732 single to 3 phase perhaps based on my 8.8 per phase 3.2kw motor

    You mentioned Trick wiring. Can you explain

    Also, does the attached chart look accurate?

    thanks again
    I don't think your 3.2Kw spindle will be 8.8 per phase

    Trick wiring, well it is not for everyone, so I only post about it when it is needed. at this point you don't have a need.

    Motor name plate Amps or FLA x 1.732= the required input Amps for Single Phase Supply to 3 Phase, plus 125% for cable and Breaker size, you can work it out from this PDF
    Mactec54

  2. #22
    Join Date
    Oct 2021
    Posts
    24

    Re: Need help ....Fuling Vfd, steel enclosure and small steps

    Quote Originally Posted by mactec54 View Post
    I don't think your 3.2Kw spindle will be 8.8 per phase

    Trick wiring, well it is not for everyone, so I only post about it when it is needed. at this point you don't have a need.

    Motor name plate Amps or FLA x 1.732= the required input Amps for Single Phase Supply to 3 Phase, plus 125% for cable and Breaker size, you can work it out from this PDF
    What do you figure my spindle will draw per phase, under 8? Manufacturer says that 120% of rated for 8 sec is max recommended.

    Unless I push it hard, I don't think I'll ever see much over 20 amps in the single phase side.

    3.2 kw @240 v (my supply voltage

    3.2/.24 X1.25 = 16.7 amps

    Distance from service to VFD is under 6 feet

  3. #23
    Join Date
    Jan 2005
    Posts
    15362

    Re: Need help ....Fuling Vfd, steel enclosure and small steps

    Quote Originally Posted by rjwims View Post
    What do you figure my spindle will draw per phase, under 8? Manufacturer says that 120% of rated for 8 sec is max recommended.

    Unless I push it hard, I don't think I'll ever see much over 20 amps in the single phase side.

    3.2 kw @240 v (my supply voltage

    3.2/.24 X1.25 = 16.7 amps

    Distance from service to VFD is under 6 feet
    If the name plate amps are 8.8A then it should be around 3A per phase
    Mactec54

  4. #24
    Join Date
    Oct 2021
    Posts
    24

    Re: Need help ....Fuling Vfd, steel enclosure and small steps

    It's as clear as mud.....lol

    I'll get it eventually, I hope

    thanks again, you are a wealth of knowledge

Page 2 of 2 12

Similar Threads

  1. Seting up a Fuling DZB VFD
    By GerryG in forum Spindles / VFD
    Replies: 13
    Last Post: 06-18-2020, 08:56 AM
  2. Fuling DZB300 series VFD and Spindle
    By BJM737 in forum Spindles / VFD
    Replies: 6
    Last Post: 12-30-2019, 04:28 PM
  3. Fuling d130m vfd
    By ezajohn in forum Spindles / VFD
    Replies: 0
    Last Post: 11-16-2014, 03:42 PM
  4. Need help: Help me identify this VFD FULING
    By rajshinai in forum Spindles / VFD
    Replies: 0
    Last Post: 08-27-2014, 08:29 AM
  5. Fuling to Huanyang VFD switch
    By futureform in forum Phase Converters
    Replies: 7
    Last Post: 05-06-2013, 01:49 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •