    Spindle motor wiring diagram

    I have a spindle motor with the following motor tag. I'll be using the rating in the box - 230v @ 50 hz.

    Attachment 473540



    The diagram from the cover showing how to jump the leads; seems simple enough.

    Attachment 473542



    Here's where I'm confused. Both the motor on the machine and the spare that came with it are wired like this.

    Attachment 473544


    Obviously it's easy enough to change the jumpers around but neither motor is wired to match either of those two diagrams. If they were wired for high voltage the power should be coming in on the UVW-1 side and the UVW-2 should have the jumpers but as they are, it's reversed. Both motors had those covers and they were both the same. Should I shrug it off, wire it up the way I need it and move on with life or does this hint at a concern I should have?

  2. #2
    Join Date
    Mar 2009
    Posts
    1982

    Re: Spindle motor wiring diagram

    on the label of your motor 230VAC is for delta (triangle) connection. Means, you need to connect jumpers "three in parallel" way, as drawn in framed picture.
    The motor connection on the last bottom illustration is "star", ( opposite to "delta" ). "Star" connection used by default everywhere because windings are connected in series in regards to applied voltage - less chances of overcurrent.

  3. #3
    Join Date
    Dec 2003
    Posts
    24220

    Re: Spindle motor wiring diagram

    Quote Originally Posted by ecdez View Post
    I have a spindle motor with the following motor tag. I'll be using the rating in the box - 230v @ 50 hz.

    The diagram from the cover showing how to jump the leads; seems simple enough.

    Here's where I'm confused. Both the motor on the machine and the spare that came with it are wired like this.


    Obviously it's easy enough to change the jumpers around but neither motor is wired to match either of those two diagrams. If they were wired for high voltage the power should be coming in on the UVW-1 side and the UVW-2 should have the jumpers but as they are, it's reversed. Both motors had those covers and they were both the same. Should I shrug it off, wire it up the way I need it and move on with life or does this hint at a concern I should have?
    IOW, The method of using either the U2 V2 W2 or U1 V1 W1 for the straps will be identical electrically.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. Stepper Motor Controls Wiring Diagram
    By hachin in forum CNC Machine Related Electronics
    Replies: 5
    Last Post: 11-29-2023, 05:54 AM
  2. Replies: 0
    Last Post: 05-16-2019, 06:04 PM
  3. Wiring diagram for 24v DC motor to ESS controller
    By masinecc in forum CNC Plasma / Oxy Fuel Cutting Machines
    Replies: 0
    Last Post: 01-21-2018, 07:52 PM
  4. Trying to ID this Breakout board/Spindle Wiring Diagram
    By Barefootboy4 in forum Spindles / VFD
    Replies: 0
    Last Post: 12-27-2017, 10:57 PM
  5. ATR Manufacturing MC-40 motor controller wiring diagram.
    By Galane in forum CNC Machine Related Electronics
    Replies: 0
    Last Post: 06-01-2015, 12:20 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •