I have some sheets, but the answer is fairly simple,after all it is feeding both amplifiers and to take advantage of the thermal sensor for both drives, you would have to connect two wires in the CN2 that only has the three wires and connect them in parallel to the terminals on the transformer TOH1&TOH2, but I do not know the implications of this (parallel two drive inputs).
But I do not think you need to go this route, as lets say you just jumper the 4&5 terminals out in the CN2 that only has 3 wires.
Either drive can cause overheat of the transformer, and as long as one of them is monitoring the thermal sw. the system will go in to E-stop regardless if it is the other amp causing the overheat problem.
I would tend to go the jumper route, the one down side is IF the thermal switch opens because of overcurrent of the opposite amp, the companion amplifer will be the one reporting it in the alarm.
M.