    Single vs 3 Phase input on Huanyang VFD

    Hi,

    Was looking to replace a broken HY0D223B Single Phase Input 2.2Kw
    Accidentally picked up a HY0D243B 380v input 2.2 Kw

    I was just interested if someone knew where the differences were and if there was any way to do an easy converstion.
    Intrigued as to why the HY0D243B exists when the HY0D223B takes single or 3 phase input anyway - though I notice the output current is different by a factor of 2 - when would that be helpful please.

    From having a look the boards look pretty much identical apart from some components that could just be a updated revision.

    We have hooked it up and, unsurprisingly, are getting an E.Lu.S error.

    Many thanks

  2. #2
    Join Date
    Jan 2005
    Posts
    15362

    Re: Single vs 3 Phase input on Huanyang VFD

    Quote Originally Posted by richmondmakerlabs View Post
    Hi,

    Was looking to replace a broken HY0D223B Single Phase Input 2.2Kw
    Accidentally picked up a HY0D243B 380v input 2.2 Kw

    I was just interested if someone knew where the differences were and if there was any way to do an easy converstion.
    Intrigued as to why the HY0D243B exists when the HY0D223B takes single or 3 phase input anyway - though I notice the output current is different by a factor of 2 - when would that be helpful please.

    From having a look the boards look pretty much identical apart from some components that could just be a updated revision.

    We have hooked it up and, unsurprisingly, are getting an E.Lu.S error.

    Many thanks
    It exists because they have 380v spindles

    E.L.U.S is a supply voltage problem or missing phase

    The VFD Drive is looking for 380v, it is no good to use unless you have 380v / 400v 3 Phase power.

    See if you can return it.
    Mactec54

  3. #3
    Join Date
    Jun 2010
    Posts
    4256

    Re: Single vs 3 Phase input on Huanyang VFD

    There is NO easy conversion.
    There is NO conversion path at all.

    Cheers
    Roger

  4. #4

    Re: Single vs 3 Phase input on Huanyang VFD

    Suspected as much but hope you appreciate why I'd check. I'll keep it for when we get 3 phase and a new project.

    Thanks for taking the time to answer both.

Similar Threads

  1. VFD single phase input three phase output
    By ZeroBacklash in forum Spindles / VFD
    Replies: 42
    Last Post: 07-26-2018, 05:22 PM
  2. Correct VFD for 5HP Motor with Single Phase Input
    By JJ0704 in forum Spindles / VFD
    Replies: 30
    Last Post: 07-15-2018, 04:44 AM
  3. Replies: 0
    Last Post: 05-02-2015, 07:56 AM
  4. Replies: 14
    Last Post: 05-23-2013, 07:59 PM
  5. 3 phase input VFD for single phase input?
    By Redhead in forum Phase Converters
    Replies: 4
    Last Post: 02-27-2008, 05:30 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •