    Question 18i-TA plc inputs lost on a Mori seiki SL300

    Hi
    Have anyone an idea why the first inputs from X0.x to X3.7 is lost from X4.0 they works . The first 0.0 to 3.7 is going directly to the PLC card and the others goes trough I/O modules .
    have tried to exchange the PLC ( which also have the spindle monitor) A03B-0814-B101, but no change

  2. #2
    Join Date
    Feb 2006
    Posts
    19

    Re: 18i-TA plc inputs lost on a Mori seiki SL300

    Are there any error messages?
    You might have a short circuit on one of the inputs from x0.0 to x3.7 that is dragging the whole group down. Try disconnecting them byte by byte

  3. #3
    Join Date
    May 2019
    Posts
    10

    Re: 18i-TA plc inputs lost on a Mori seiki SL300

    Hi , thanks for reply .
    short ? do you mean that one of them are connected to gnd (-24). I will check with my customer tomorrow about the alarms . It's 7hours trawell 1 way to him , so I hope to help him by phone , he have some clever electricians , that can pull the plugs , if i tell them which ones .
    regards Ulf

  4. #4
    Join Date
    Aug 2019
    Posts
    145

    Re: 18i-TA plc inputs lost on a Mori seiki SL300

    The 18i-A has several I/O types available. What is the specific I/O unit you are working with. Depending on the unit there could be internal fusing or jumpers that select sinking or sourcing.
    Reference the OEM prints and see if its possible a common or source voltage wire has come loose for those inputs and the I/O device the connect to.

    Its also possible that a short damaged the unit those inputs are on.

  5. #5
    Join Date
    May 2019
    Posts
    10

    Re: 18i-TA plc inputs lost on a Mori seiki SL300

    have now exchange PLC Card ( actually a combined spindle control and I/O A03B-0814-B101 ) and the Interface card between the CNC and the PLC .,
    measured the cables between . and reloaded the SRAM backup. but still the same ...??

  6. #6
    Join Date
    May 2019
    Posts
    10

    Re: 18i-TA plc inputs lost on a Mori seiki SL300

    Have found that this I/O s is not shown on the PMC , you can only see them directly wit a special fanuc reader connected to the PLC directly. However the problem was not the card and it was bad contact in the plugs to the safety module + defective nc contact on the KM1

Similar Threads

  1. Mori Seiki SL-153 Fanuc 18i TA
    By TD3569 in forum Fanuc
    Replies: 3
    Last Post: 01-06-2021, 03:03 PM
  2. Mori Sl300 programming
    By Rob okuma user in forum Mori Seiki lathes
    Replies: 16
    Last Post: 01-15-2013, 12:21 PM
  3. Mori Seiki JR PLC programs
    By Nikola in forum Mori Seiki Mills
    Replies: 12
    Last Post: 11-01-2010, 09:44 PM
  4. Replies: 2
    Last Post: 01-25-2010, 05:14 PM
  5. Replies: 6
    Last Post: 03-20-2007, 03:54 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •