    Hello guys,
    I am new to the group and I am facing an issue with my new huanyang VFD
    The spindle is: 400Hz, 24000 rpm, 1.5Kw, 8A, 110V. 3phases 2 poles
    VFD MODEL: HY01D511B, 110V-110V, 1.5KW, 13A
    The first time I tried to run the spindle, the spindle turned for like 15 minutes and then stops, VDF shows E.o.L.A error
    I tried these settings before:
    PD001 = 1
    PD002 = 1
    PD003 = 400 = Main frequency
    PD004 = 400 = Base frequency
    PD005 = 400 = Max operating frequency
    PD006 = 3.0 = Intermediate frequency
    PD008 = 110 = Max voltage
    PD009 = 7.5 = Intermediate voltage
    PD010 = 4 = Min voltage
    PD011 = 120 = Frequency lower limit
    PD070 = 1 = Analog input
    PD072 = 400 = Higher analog frequency
    PD141 = 110 = Rated motor voltage
    PD142 = 7 = Rated motor current [motor says 8A] – Setting won’t go any higher than 7
    PD143 = 2 = Number of motor poles
    PD144 = 3000
    After these parameters, I got others which are a bit similar to the first ones but I now get the E.o.L.d error
    PD001 = 1
    PD002 = 1
    PD003 = 400
    PD004 = 400
    PD005 = 400
    PD006 = 3.0
    PD007 = 20
    PD008 = 110
    PD009 = 7.5
    PD010 = 4
    PD011 = 120
    PD014 = 10
    PD015 = 10
    PD070 = 1
    PD072 = 400
    PD073 = 120
    PD120 = 100
    PD141 = 110
    PD142 = 7
    PD143 = 2
    PD144 = 3000
    Can anyone help me to ensure I have the right parameters set.
    Thank you.
    15362
    Re: Huanyang VDF E.o.L.A/E.o.L.d Error
    Quote Originally Posted by 00chris View Post
    Hello guys,
    PD001 = 1
    PD002 = 1
    PD144 = 3000
    PD001 = 1
    PD002 = 1
    PD003 = 400
    PD004 = 400
    PD005 = 400
    PD006 = 3.0
    PD007 = 20
    PD008 = 110
    PD009 = 7.5
    PD010 = 4
    PD011 = 120
    PD014 = 10
    PD015 = 10
    PD070 = 1
    PD072 = 400
    PD073 = 120
    PD120 = 100
    PD141 = 110
    PD142 = 7
    PD143 = 2
    PD144 = 3000
    Thank you.
    Messing with fire, Parameters are incorrect, do not run it with the Parameters set like this, I will give you some to change this
    PD006
    PD009
    PD0010
    Check the wiring at the spindle plug that they have good connections, all 3 Phases must be connected, and each wire is protected from each other
    Do you have the Ground connected the 4th pin must be connected and the 4th pin has Continuity to the spindle body
    Input wiring to the VFD Drive need a Photo to check that that is correct, you must be connected to R and T plus Ground for single Phase Use on this VFD Drive
    Mactec54
    15362
    Hello guys,
    PD001 = 1
    PD002 = 1
    PD144 = 3000
    PD001 = 1
    PD002 = 1
    PD003 = 400
    PD004 = 400
    PD005 = 400
    PD006 = 3.0
    PD007 = 20
    PD008 = 110
    PD009 = 7.5
    PD010 = 4
    PD011 = 120
    PD014 = 10
    PD015 = 10
    PD070 = 1
    PD072 = 400
    PD073 = 120
    PD120 = 100
    PD141 = 110
    PD142 = 7
    PD143 = 2
    PD144 = 3000
    Thank you.
    PD006=260
    PD007=20
    PD008=110
    PD009=71.5
    PD010=5.5
    PD120= 100 to 120
    Most of your problem I think is wiring or you Power supply to the VFD Drive, it should have run with the Parmeter's you had set in the first lot.
    What is your spindle manufacture as others have been have trouble with one of the spindle brands??
    PD007 and PD010 work together as does PD006 and PD009, the V/Hz ratio must match, when using these Parameters, they can be left at Default and can still run your spindle ok
    Mactec54
  1. Huanyang VFD Over Current Error EoCA
    By nates02gt in forum Spindles / VFD
    Last Post: 06-18-2023, 04:01 PM
  2. Huanyang HY02D223B error code
    By Maslab in forum Spindles / VFD
    Last Post: 09-26-2021, 04:58 PM
  3. Copy Delta VDF settings? (VDF 022 EL 21 A)
    By stefancnc in forum Spindles / VFD
    Last Post: 03-10-2019, 01:54 AM
  4. Huanyang VFD Inverter all available Error Codes
    By Saintstone in forum Phase Converters
    Last Post: 07-08-2017, 11:26 AM