    fanuc 18mc serial port dead

    I have a Supermax mill with fa anuc 18m control.
    The machine was in a good working condition. Today I discovered that the Pc attached on its serial port does't boot any more.
    After some searching I found that the PC serial port was blown.
    From then I cant load or upload anything to or from the machine. I didnt find any other problems except this.
    When I try to PUNCH, the control seems to output with no errors and when I try to READ, LSK flashes normany.
    Pin 25 of the serial has 24v, Pin2 has about 11v and pin3 about 2v.

    Has anyone faced anything similar?

    Michael

  2. #2
    Join Date
    Apr 2009
    Posts
    1379

    Re: fanuc 18mc serial port dead

    Pin 25 of the serial has 24v: that is supplied by the control for tape punches and is not used for regular serial comms.
    Isolate whether the problem is in the control or pc.

  3. #3
    Join Date
    Jul 2010
    Posts
    46

    Re: fanuc 18mc serial port dead

    the problem is in the control or cable.
    I try to use serial port 2 (channel 2) changing the serial cable to JD5B from JD5A but with no luck, even LSK doesnt flash.

  4. #4
    Join Date
    Aug 2019
    Posts
    145

    Re: fanuc 18mc serial port dead

    Unfortunately the 2nd port is an option (although the hardware is present). If you have the data sheet you could see if it is enabled.
    Serial is notoriously sensitive and if you are not already using them I would suggest suppressor's for your cables once you get things sorted.
    Do you have the pinout to confirm the cable is good?

  5. #5
    Join Date
    Aug 2009
    Posts
    1566

    Re: fanuc 18mc serial port dead

    ...use a RS232 to IP converter unit like this to electrically (OPTO) isolate machine from PC is a good idea. Also, can access from any PC on your network.
    https://www.ebay.com/itm/40311464772...cAAOSwC0ZhK8L5
    Bad earth grounding at the machine or the PC can blow cards.

  6. #6
    Join Date
    Jul 2010
    Posts
    46

    Re: fanuc 18mc serial port dead

    I have the pinout. The cable is good, it use to work for me.

  7. #7
    Join Date
    Jul 2010
    Posts
    46

    Re: fanuc 18mc serial port dead

    I have the same IP to Rs232 MOXA that I use on a lathe. I tried it but still with no luck.

    Is it possible to find a schematic of the board A16B-3200-21 9/02A because as I keep searching, I have read that there are RS232 tranceiver ICs possibly damaged.

    Is there any other way to insert a part program into the controller except the RS232 and typing?

  8. #8
    Join Date
    Aug 2019
    Posts
    145

    Re: fanuc 18mc serial port dead

    I would pursue the option route for the 2nd port before attempting to go component level on that series of control.
    The serial hardware are 2 and 4 channel so the hardware is there for the 2nd port. It should just need to be enabled through options and setting the correct com parameters.
    20 = 2
    121 = stop bits etc.
    122 = device type
    123 = baud rate


    Other options for transfer that would use different ports are unfortunately limited (Remote buffer, Data Server, HSSB?) and all require additional hardware and options.

  9. #9
    Join Date
    Jul 2010
    Posts
    46

    Re: fanuc 18mc serial port dead

    I have already tried this, but LSK doesnt flash when start receiving.(btw, I use @122 as device type 0.Is it right?)

  10. #10
    Join Date
    Apr 2009
    Posts
    1379

    Re: fanuc 18mc serial port dead

    I have the schematics A16B-3200-0210 and successfully repaired such problems on other controls. Send me an email: [email protected] and I'll scan the page with the serial on it.

  11. #11
    Join Date
    Jul 2010
    Posts
    46

    Re: fanuc 18mc serial port dead

    I have found the blown ICs and diodes in order to repair the damage.
    Also changed to serial port 2 and now it is working.
    Thank you all

  12. #12
    Join Date
    Oct 2018
    Posts
    7

    Re: fanuc 18mc serial port dead

    Hi Magzi , i have the exact same problem, could you please tell me how did you manage you use the port 2?
    Thanks in advance

  13. #13
    Join Date
    Jul 2010
    Posts
    46

    Re: fanuc 18mc serial port dead

    set parameter 9934.4 to 1 (=enable JD5B)
    i/o channel to 2

  14. #14
    Join Date
    Apr 2009
    Posts
    1379

    Re: fanuc 18mc serial port dead

    That parameter is for the remote buffer board.

  15. #15
    Join Date
    Dec 2009
    Posts
    947

    Re: fanuc 18mc serial port dead

    Quote Originally Posted by magzi View Post
    set parameter 9934.4 to 1 (=enable JD5B)
    i/o channel to 2
    Please do not share public this option parameters
    that must be send by private message to everyone you want to help
    Thanks for understanding

Similar Threads

  1. Serial spindle is dead in Fanuc-o-md
    By moghul in forum Fanuc
    Replies: 0
    Last Post: 09-08-2011, 05:06 AM
  2. Connecting Fanuc 11M via Serial Port
    By Tenretni in forum Fanuc
    Replies: 2
    Last Post: 03-08-2010, 03:48 AM
  3. Help! Dead CNC serial port when receiving!
    By DerHammer in forum Fanuc
    Replies: 39
    Last Post: 08-23-2007, 12:20 AM
  4. Serial Port Issues with GE Fanuc OT-C
    By keystoneprec in forum Fanuc
    Replies: 7
    Last Post: 04-05-2007, 03:39 PM
  5. Fanuc 0T Serial port problem
    By a_greavu in forum Fanuc
    Replies: 3
    Last Post: 10-12-2006, 11:31 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •