    Changing MC-4VA from 480 to 220V

    I need to change my new to me machine to 220 3ph from 480V.
    It looks like power comes into the main on/off switch, then goes to a multi tap transformer assembly next to the ATC.
    I think I just need to reposition the three bus bars to the 220v position to change the machine to 220v. Is this correct?
    The machine came with a 277/480 surge protector, but I guess i'll have to get a 220v delta unit instead.

    I ordered a phase rotation tester. I'm assuming if I connect the input wires in the "clockwise" rotation everything should be OK?
    Also, the rotary phase converter instructions don't recommend using the manufactured leg to power the controls and so on. Instead, to use L1 and L2 to power the controls. Is this possible or does this machine use 3ph for the controls? If not, which leg should I attach the manufactured lead to?

    Is there any way to verify I have the power leads connected in the proper rotation?

    Thanks,
    Bryan

    Click image for larger version. 

Name:	voltage conversion bus.jpg 
Views:	0 
Size:	102.8 KB 
ID:	489952

  2. #2
    Join Date
    Apr 2009
    Posts
    1262

    Re: Changing MC-4VA from 480 to 220V

    You are correct that moving the taps to the required voltage indicated will work.

    Phase can be confirmed by checking for hydraulic pressure. If that builds then phases are correct.

    I believe that the middle leg should go to the manufactured leg if I remember correctly.

    The control should be running off of the 24v power supply. 110 is only used for the fans and lights on your machine.

    Best regards,
    Experience is what you get just after you needed it.

  3. #3
    Join Date
    Nov 2013
    Posts
    23

    Re: Changing MC-4VA from 480 to 220V

    After poring over the schematics, it looks like the 3rd leg is the one to use.
    L1 and L2 are used for the single phase loads.
    Quite a bit of stuff is 3 phase, including the spindle control, axis motors control, hydraulic pump, coolant pump, spindle lube pump, way lube pump & oil temp controller.
    A bunch of stuff goes through a triple coil transformer in the equipment cabinet. It has output windings for a 120v & 100v outputs and three 24v outputs. Don't really know if the 3rd phase passes through or not. I don't really understand how this transformer works. Certainly 3ph input, but five separate output coils? Do input phases correspond to any of the specific outputs?

    Thanks,
    Bryan

    Click image for larger version. 

Name:	transformer wiring diagram.jpg 
Views:	0 
Size:	93.7 KB 
ID:	490339

Similar Threads

  1. 220v Chinese motor both hot leads need to be 220v?
    By CNCgenie9910 in forum Laser Engraving / Cutting Machine General Topics
    Replies: 8
    Last Post: 01-16-2024, 05:21 AM
  2. Replacing AC 220V motor with AC 220V servomotor, how to choose?
    By gapimankr in forum Servo Motors / Drives
    Replies: 2
    Last Post: 01-02-2016, 08:22 PM
  3. Bridgeport R2E3 delima, 220v VFD 3 phase Versus 220V Single Phase
    By ronderkis in forum Bridgeport / Hardinge Mills
    Replies: 7
    Last Post: 03-25-2015, 04:01 AM
  4. Replies: 8
    Last Post: 12-21-2014, 01:49 PM
  5. Mach3 PWM Spindle Speed Control using 220v 1ph VFD/220v 3ph spindle motor.
    By Ozzwinkle in forum Mach Software (ArtSoft software)
    Replies: 4
    Last Post: 12-23-2013, 07:01 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •