Hi!
our john ford St60B machine is giving NC alarm 510 (overtravel X+)when it zero returns.
system is : fanuc 0M
any help.
Hi!
any help.
alarm is 510 which says: overtravel X+.
Machine model is: JOHN FORD ST60B
system; Fanuc 0M
any help
Switch on the NC while press and holding P and CAN key.And you can do reference.
Hi!
by mistake i wrote it crosses hard limits.it does not.
simply put pressing CAN & P has no effect at all.
The P Can while powering up tells the NC to ignore soft limits that are set in parameters. This allows the machine to make it to limit switch and set zero position. If you are overtraveling at this point you should look at the limit switch and ensure it is functioning properly.
Bob
Do you mean that it always hits the over travel switch when you "zero home"?
If so, the home switch is not working.
Param. 65 bit#3 befor a reference position is made,the stored stroke limit is checked(0)/is not checked(1)
Param. 700 to 703 First stored stroke limit in the positive direction on each axis
Param. 704 to 707 First stored stroke limit in the negative direction on each axis
Limit switch for x-axix was ok.its wire connection with the T002D card in electrical cabinet was broken somewhere in between.when corrected machine was referenced uning CAN & P combibation and its working now.
thanks all
P and CAN worked for me!!! Thanks lots
which parameter is for +z axis #700 to adjust the reference point, cause ATC ARM hits z-axis when tool change. I need to move z axis a little bit up