    Hall sensor connection

    Hi all,

    I have a question on hall sensor connection.

    I have an electric actuator with the following connection




    The hall sensor is supposed to connect to a PLC NPN input. The RED and BLACK goes to 24VDC and 0V DC respectively, YELLOW goes to my PLC input (which the PLC input common is pull high to 24VDC).

    However, The PLC can't "read" the signal from YELLOW. Sadly I do not have an osciloscope.
    While the actuator is moving, I measured across the YELLOW and BLACK and I get voltage like 12V, 17VDC....

    Did I miss out anything?

    Thanks all.

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    You have a source device so your PLC should be sink input.
    Did you tie the GND to your PLC common?
    with the load resistors in place, you should get a high to low reading on the sensors without any connection to the PLC.
    Monitor with a voltmeter between common and Yellow, by turning the motor etc as slow as possible, before connecting to PLC.
    If you turn slow enough you should be able to read a 24v to 0 transition, too fast and it will be anywhere in between.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. Hall Effect Chopper
    By legomanww in forum CNC Machine Related Electronics
    Replies: 5
    Last Post: 12-20-2007, 09:11 AM
  2. Hall Effect Limit & Zero
    By Trebleplink in forum CNC Machine Related Electronics
    Replies: 3
    Last Post: 10-20-2007, 12:08 AM
  3. where can I buy encoders w/Hall for brushless motors for reasonalbe?
    By springlakecnc in forum CNC (Mill / Lathe) Control Software (NC)
    Replies: 3
    Last Post: 09-17-2007, 10:05 PM
  4. Hall encoders
    By danSN in forum Servo Motors / Drives
    Replies: 2
    Last Post: 11-28-2006, 04:24 PM
  5. C-D track to Hall conversion
    By interflexo in forum Servo Motors / Drives
    Replies: 0
    Last Post: 07-30-2006, 01:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •