    Fanuc 10T startup problem

    Mori Seiki TL-40 with Fanuc 10T. I am getting a "PC 010 PC ERROR" alarm during power up most of the time. Fanuc says I need a new memory cassette which costs about $3500. Is there a less expensive way to correct this? The last line displayed during the start sequence before the alarm is "Loading PC Parameters: End"

  2. #2
    Join Date
    Dec 2003
    Posts
    24221
    If this is the PMC cassette, Fanuc usually load the PMC in from the Eproms in the cassette and then run the ladder from ram memory.
    I have picked up a cassette off ebay for $16.00, but you need to transfer your eproms over, if it is the eproms themselves then you are out of luck and would need to obtain a fresh copy of the ladder in eprom.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Apr 2009
    Posts
    10
    Thank you, I will try that.

Similar Threads

  1. 5020L startup problem
    By rick kroeze in forum Okuma
    Replies: 3
    Last Post: 07-31-2009, 08:36 PM
  2. KM3P problem startup
    By jimc80 in forum HURCO
    Replies: 2
    Last Post: 07-09-2009, 07:38 PM
  3. HAAS VF1 Startup Problem
    By rkdygert in forum Haas Mills
    Replies: 8
    Last Post: 07-25-2007, 12:59 AM
  4. Startup Problem
    By StormWerkz in forum Fadal
    Replies: 14
    Last Post: 03-07-2007, 04:57 AM
  5. Hurco BMC 20 startup problem
    By tirebiter in forum DNC Problems and Solutions
    Replies: 3
    Last Post: 11-08-2006, 11:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •