545,767 active members*
1,840 visitors online*
Results 1 to 5 of 5
    Junior Member
    Jul 2015
    13
    VFD 110V-110V parameters setting
    Hello guys,
    I have a Huanyang VFD 100v-110v and I need help for parameter settings.
    I need to set it to be controlled by USB CNC controller board and connect to spindle.
    The spindle is:
    GDZ-15, Diameter 65mm, H160mm, 400Hz, 24000 rpm, 800w, 6A, 150V.
    VFD MODEL: HY01D511B, 110V-110V, 1.5KW, 14A
    I tried these settings before:
    P0=0
    P1=1
    P2=1
    P3=400
    P4=400
    P5=400
    P8=150
    P70=0
    P72=400
    P73=0
    P141=150
    P142=6A
    P144=24000
    P142=6
    After putting these parameters, I don't know how to activate them because the VFD screen remain blinking (see picture)
    After these parameters, I got others which are a bit similar to the first ones but the VFD screen remain blinking an on the picture:
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
    PD001=0 (1 For Remote Control)
    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220 (120 If you have 120v VFD )
    PD009=15
    PD010=8
    PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
    PD014 Acceleration=12 ( Adjust to suit)
    PD015 Deceleration=12 (Adjust to suit)
    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
    PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
    PD142= ( Motor Max Amps)
    PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
    PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
    PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
    PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )
    PD143=2 ( Motor Number of Poles)
    PD144=3000 (Max Motor RPM) =3,000= (24,000)
    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
    PD72=400
    PD73=120 ( 100 Minimum Setting )
    So, I realy need help to set up this VFD.
    Thank you in advance
    Jan 2005
    12538
    Re: VFD 110V-110V parameters setting
    Quote Originally Posted by Gautier View Post
    Hello guys,
    The spindle is:
    P0=0
    P1=1
    P2=1
    P3=400
    P4=400
    P5=400
    P8=150
    P70=0
    P72=400
    P73=0
    P141=150
    P142=6A
    P144=24000
    P142=6
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD009=15
    PD010=8
    PD72=400
    What does your parameters start with you have 2 that are different are they PD or something else, you have to use the correct parameters for the VFD that you have, how do you have it wired
    Mactec54
    Junior Member
    Jul 2015
    13
    My parameters start with Pd. For example Pd001.
    The spindle is:
    Attached is the wiring diagram picture and picture of VFD's state (blinking screen) after putting the parameters. I verified several times and the wiring is fine.
    I followed some videos on youtube concerning Huanyang VFD and found that after setting parameters the user need to hit the "RUN" button and the screen stops blinking; but for me it doesn't stop blinking, it remains blinking even if I hit the RUN button.
    I realy need help to configure this VFD.Click image for larger version.
ID:	403613Click image for larger version.
ID:	403615Click image for larger version.
ID:	403617Click image for larger version.
    Company Representative
    Oct 2005
    858
    Pls email to us, we will help you to set up
    We have this VFD in stock we can simulate it
    https://www.automationtechnologiesin...e/cnc-spindle/
    https://www.automationtechnologiesin...ooled-spindle/
    Jan 2005
    12538
    The spindle is:
    Using the internet can get you into trouble most show you incorrect settings, turn it off wait about 1min and turn it on again press the stop button/reset if this does not work for you, on some of these HY drives you can remove the Key Pad and then replace it if this does not fix the problem contact the seller as you have a faulty drive
    Your attachments do not open
    Mactec54
    Junior Member
    Jul 2015
    13
    Hello guys,
    I thank you for your help. Especially "Automationtechnic". Now I am able to run the spindle using the VFD's panel control. Now I need to run it using the USB CNC controller card (see picture). As Automationtechnic told me that they are not familiar to USB CNC controller board, I still need help in order to control the VFD through USB CNC controller:
    1. How to connect the VFD and USB CNC? and the position of jumpers on USB CNC board; or if the attached picture is correct?
    2. Which VFD parameters to change?
    3. Do I need to change the VFD's jumper from VR to VI position?
    4. Which settings to make inside the Planet USB CNC software in order to control the VFD?
    These are the parameters which are working now but using the VFD's panel (from automationtechinc):
    PD001 = 0
    PD002 = 0
    PD005 = 400
    PD004 = 400
    PD003 = 400
    PD141 = 110 or 220V ( check the spindle rate)
    PD142 = 11.0 or 5A
    PD144 = 2800
    PD008 =110
    PD013=1
    PD072=400
    Attached is the board
Name:	CNC USB Connexions.jpg
    Jun 2021
    Good day I have purchased this "2.2KW Water Cooled Spindle Motor ER20 24000rpm 400Hz+2.2KW VFD Inverter Variable Frequency Driver 110V" and parameters Pd 003 Pd 004 Pd 005 Will not change from 50.. can someone help pls
    thanks
    Jan 2005
    12538
    Quote Originally Posted by ACERO1 View Post
    thanks
    Who would buy a 2.2Kw to run on 120v single phase supply ???
    Have you checked the Parameter Lock
    PD000=0 needs to be zero or this will lock the Parameter Settings
    Mactec54