If the 24VAC secondary taps on the transformer have no significant voltage coming out; but you are putting between 208VAC and 240VAC into the primary-side taps, then your transformer has burnt out...
Type: Posts; User: cncsnw
If the 24VAC secondary taps on the transformer have no significant voltage coming out; but you are putting between 208VAC and 240VAC into the primary-side taps, then your transformer has burnt out...
I have been working with a customer's 1986-1987 CHNC II+, and am trying to help him understand the axis lube system.
There is the usual air-pressurized way lube tank under the left end of the...
Jay,
It would be very difficult to make a useful guess about this, without knowing more about the control; how it is configured; what PLC program it is running; etc..
Fortunately, Centroid...
Regarding your Z issue, you might look at Machine Parameter 130, and the possible use (intentional or unintentional) of a 3-Axis / 4-Axis function key on the F1/Setup menu.
Regarding your cutter...
You can use the Profile cycle without going to, or past, X0.
The first move in the Profile still needs to move only X, but that could be as short as going from clearance to the stock OD. Then you...
What diameter value do you have in your offset library for D6?
For future reference, here is what I found about interfacing Fadal AMP0034 and AMP0040 AC drives with a Centroid control.
1) It is more straightforward to use an MPU11 and GPIO4D combination,...
If nothing happens when you press Cycle Start to find home, then your jog panel is malfunctioning or disconnected.
If, on the other hand, an error or fault or stall message appears in the status...
Interesting. I didn't think it was possible for the CNC12 control software to report a spindle fault, without a "SpindleOk" input defined.
If you continue to have difficulty, post on the Centroid...
What Acorn input did you define for "SpindleOk"?
What VFD terminal did you connect to that input?
What value do you have in F1.13 or F1.14, as applicable?
You could use a USB-to-RS232 adapter on the sending computer, plus an RS232 cable, plus DOS-based serial file transfer software on the control computer, such as my NWDNC program, to transfer files. ...
It is not clear to me whether you replaced wires, or optical fibers.
However, that is not particularly important. Wire or fiber connections between the console and the control cabinet would...
Can you post Report files from both controls, and tell on which feed hold stops the spindle, and on which it does not?
On most Centroid controls (i.e. all with typical PLC programming), Feed Hold...
The ALLIN1DC would definitely be a nicer solution. It has the same mounting footprint as the SERVO3IO, and would allow you to use the existing servo power supply, and to use the existing motors and...
I am not sure where to begin.
You do not run the motor power through the little blue relays on the Acorn expansion board. You run the motor power through contactors, like those in the bottom...
You could continue to use the existing across-the-line starter (reversing contactor set). You would just need to run the coil power for the contactors through PLC relay outputs.
Alternately, if...
Is the spindle motor really a single-voltage 550VAC motor? If so, and if you are not in a Canadian industrial site or other location that has 600VAC service, you may have trouble powering it,...
Doesn't the Glentek drive use 5VDC logic for its enable (actually an inhibit) input and its fault output? You might find it challenging to interface that with the Oak, which expects 24VDC logic.
...
If the limit switch inputs (INP3 and INP4 for Y, INP5 and INP6 for Z) all show green on the Alt-i PLC Diagnostic display, and they do not have white bars above them (indicating the circuits are...
Can you jog the X axis without errors (e.g. in Slow, Continuous jog mode, without trying to home the machine first)?
If not, then it is probably a servo drive or servo power problem, or a problem...
See https://centroidcncforum.com/viewtopic.php?f=60&t=3377
No.
There is a 0-10V analog voltage output, normally used for spindle speed control, which can be used for other purposes on a machine with no spindle.
If your laser requires PWM, then you...
If the green UV and USV LEDs are out, even though you have 120VDC going into the VM+ and VM- ("GND") terminals, then there is a problem on the drive board. Possibly a blown fuse on the drive board,...
I, or Centroid, or most any other dealer can provide a replacement encoder for $240.
You would need to verify the diameter of the motor stub shaft that it clamps on to.
On the PID Configuration screen (F1/Setup -> F3/Config -> F4/PID) see the "Abs Pos" column for the affected axis. Also note the asterisk ('*') next to the axis label in the left-most column.
The...
Soft limits are on the Jog Parameters menu (F1 from Machine Configuration). They are signed distances from Machine Home.
They are only as good as your ability to set Machine Home in the same...
You need to change the 4th axis label (on the Machine Configuration -> Motor Parameters table) to 'N', to indicate that the fourth axis is not installed.
You need to connect the #4 and #5 (DATA...
It sounds like the mist coolant logic may be missing from your PLC program. Impossible to tell, though, without seeing the PLC program.
Different Ajax. This forum relates to the "Ajax" division of Centroid CNC controls.
Perhaps you could try a forum about Fagor controls, or contact Ajax Machine Tools in the UK, if that is who...
Not all brands and models of USB drive work with that version of Linux.
See if you can lay hands on a SanDisk Cruzer, preferably an older one with 4GB or less capacity.
It should show up in the...