PM me your email and I can help, there are a few sets of batteries in that control, but could be other issue
Hello!
PM me your email and I can help, there are a few sets of batteries in that control, but could be other issue
Sorry I couldn't PM. Settings were compromised i guess. My mail
[email protected]
I upload Backup for HITACHI VK45II and VM40II in my home page.
You can find it in Index of /~aike/docs
HITACHI SEIKI VG45 STANDBY problema
Buongiorno,
Mi lampeggiavano i numeri sul monitor allora o spento e riacceso completamente il cnc, ma a questo punto cliccando il tasto standby mi rimane lampeggiante quinti fa partire la pompa idraulica ma non i motori/azionamenti sembra che ci sia un'interruzione, tentano di avviarsi ma dopo circa un secondo cadono( non ho allarmi) tranne quelli vecchi tipo controllo olio lubrificazione che non vanno via perchè non riesco a superare la fase di accensione potete aiutarmi grazie
Su LADDER vedo un'interruzione
sul parametro 380.6 cos'è questo parametro?
Hi!
Please write in English. Google show me bad translation from Italian.
Hello. I can't open these files. Can you upload in another format? Thank you
Hello.
We have Hitachi Seiki Vm 40II with Seicos 3 control. I just enabled the DNC and I would really appreciate it if somebody could let me know which parameter I should change to enable helical interpolation, spiral milling. It is an option and as far as I know one of the parameters higher than 9000 should be changed.
Thank you.
- - - Updated - - -
Hello.
We have Hitachi Seiki Vm 40II with Seicos 3 control. I just enabled the DNC and I would really appreciate it if somebody could let me know which parameter I should change to enable helical interpolation, spiral milling. It is an option and as far as I know one of the parameters higher than 9000 should be changed.
Thank you.
Hi all. Please tell me what to do, an error has appeared on the machine 1040 (8000) ASV1C alarm ram error.
Hello shas595
Thanks for your time. I hope you can help me
I have the same problem (DIRECTORY BROKEN). It is a Hitachi lathe that lost parameters. We have the parameters printed. They were loaded manually.
but in the end this broken directory alarm appears
my email is [email protected]
Hi all. Please help someone who can, Hitachi Seiki HiCell 23B. Please share the machine parameters, my B axis is not displayed and the sub spindle is not controlled.
Hello. Please help. Hitachi Seiki HT20S2 with Seiki
MULTI control. I am getting 3 alarms."ALARM 362
Z-AXIS PG ERROR * SEE OPERATION MANUAL (6-1)".
"ALARM 322 CMOS VACANT AREA ERROR".
"ALARM 310 POWER FOR SERVO NOT SUPPLIED* RESET EMERG.
THEN DEPRESS STANDBY.
The STANDBY light is not lit after pushing RESET
And then STANDBY.
It looks like the Z-AXIS clutch is engaged and the
Proximity switch above the clutch is red. That servo
Motor does not appear to be engaged. Please help.
Hello!
Is the servo drive on for the Z?
It’s possible you lost some parameters due to power loss or weak battery. Parameter #6001 d3 is enable CMOS spare area check function. You can change it to a 0, reboot , turn off and change to a 1 and see if it clears. If not you might need to regenerate the control and renter all parameters.
I would advise making a backup now before anything else
John
Sent from my iPhone using Tapatalk
Thank you for the help John.
There are 2 208VAC power supplies to both servo
drives, a single phase and a 3 phase. The single
phase is at the drives' terminals. The 3 phase is
controlled by a contactor "MS-SV". THAT contactor is
not energized as it is controlled by relay "SVMX".
That relay is not energized and controlled by the
LX-3 I/O board. So to answer your question the servo
drive is NOT turned on, even though some LEDs on the
drives are lit.
Can I use one of the RS-232 ports to make a complete
digital backup of the drive? What is the procedure to
make the digital backup. In the the machine's record books I have found a couple paper backups of some of 6000
thru 7082 parameters. I will have to do some comparison
to see if they are the same and how they compare to what's in the machine control. Besides the parameters, what
else do I need to be concerned of losing?
Again, thank you for you help.