Re: HY03D023B Starts up and stops immediately without error
Originally Posted by
M_bender
Hi all,
I used an external potential free relays and repogrammed the Multi Port Inputs. All worked well for years.
Without any change on the wiring,... I started to act weird. The motor did not start, stopped randomly,...
Today I had some time to look at it and thought maybe one of the relays is damaged. I discconnected the relays and just a simple jumper cable to bridge the run signal. Same behavior. The motor starts, runs for 2-3 seconds and then shots controlled down. It is not a hard shut down, the ramp times for acceleration and stop are honored.
I thought it would be the motor and switched the run signal to the operator panel. When I start the motor with the operator panel it works just fine.
My thought is, that some of the terminals or the controller behind the terminals is damaged.
Mike
What is meant by 'Potential relay' the only ones I am familiar with is current operated for AC motor start sequence?
It does sound as thought there is an issue with the VFD PLC input ? Especially if a direct jumper does not work,
IOW, if running direct off of the panel does not work, then it could be some issue with the Opto inputs or in the PLC logic circuit.
Which if so, may not be an easy fix.