    Talking Parallel port Isolation

    I talked to Tom about parallel port isolation, he has said that it does not seem to matter. He did comment that he has heard that the Campbell board could give some issues. If others are using breakout boards or some type of parallel port isolation, if you could post your results. This would help myself and others for just the knowledge of what is being used.
    Thanks,
    Richard Konnen

  2. #2
    Join Date
    Jun 2003
    Posts
    3312
    With properly laid out system and wiring, you don't have to have opto isolation. The key is the negative/neutral/motor/driver common and current paths. Also what you plug your pc 120V into vs your drive electronics 120VAC and motor power supply 120VAC plugs into. I would venture to bet there are a number of setups that do have opto isolation, but have defeated it in their wiring via negative/common wiring.
    Phil, Still too many interests, too many projects, and not enough time!!!!!!!!
    Vist my websites - http://pminmo.com & http://millpcbs.com

  3. #3
    Join Date
    Mar 2005
    Posts
    1136
    Phil, can you elaborate a bit or suggest a solution or where people go wrong with it?

    I'm not sure I reading this right - are you saying that spikes etc (or whatever you're trying to isolate from) could reach the pc through the neutral line of the house/shop wiring? wouldn't any electrical motor with its collapsing field potentially cause the same spike and isn't it the pc's power supply's job to deal with these?

  4. #4
    Join Date
    Oct 2003
    Posts
    170
    Gentlemen,

    The opto isolated mother board is primarily targeted towards PC's that have less than a 5 volt output on the parallel port.

    Every user should use a transformer to get the VM for the motor power. As long as the user does not connect the secondary of this transformer to anything there should be no issues of spikes or anything else that would create a need for isolation.

    If a user were to rectify power straight from an outlet for their VM there could be ground loops that could damage equipment. It should NEVER be done this way.

    Tom Eldredge
    Rutex LLC
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  5. #5
    Join Date
    Jun 2003
    Posts
    3312
    One of the issues with non isolation is where is 0 volts. Sometimes I like to use extremes to illustrate a point. Fundamentally, wire has resistance and ohms law applies.
    DON"T DO WHAT I DEPICT HERE STRICTLY HYPOTHETICAL TO EXPLAIN
    Consider you have one wire from the motor power supply negative to drive X, from drive X to drive Y, from drive Y to drive Z then to the PC. Each drive handle 6A worth of motor. Each drive wire segment is .2 ohms. Ohms law is E=I*R so what you have in drive currents is 6A from the Z segment to the Y segment, 12A in the Y segment to X segment and 18A in the X segment to the Power supply. That means that the 0V at the power supply negative terminal, is actually 3.6V at the first drives negative terminal, 6V at the second drives negative terminal, and 7.2V at the Z drives negative terminal, which is wired to the PC PPort common. In all probablility the PC common is tied to safety gnd, and in good practive the power supply negative terminal is wired to safety gnd. So now now have a loop via you ac wiring safety gnd. The wire segment from the Z drive to the pc is probably going to pull a hefty current as there maybe parallel wiring in the cable and connections to/from the db25. You think this is just signal wiring, NBD and the next thing you know you power up, smell smoke, see you parallel cable wire smoking or fused open cause it was too small to handle the current.
    If the drives are optically isolated and treated properly that last wire segment (Dark green)doesn't exist.

    Tom I respectfully disagree. Optoisolation has nothing to do with the logic level output of the pc. 2nd leaving a transformer dc output not referenced to a saftey ground requires special physical isolation and insulation handling if it is to meet NEC an UL code requirements. Anytime you have a insulation fault condition that can expose 50V (I think that is the current threshold) to a conductive enclosure it has to fault.
    Attached Thumbnails Attached Thumbnails badwire.gif  
    Phil, Still too many interests, too many projects, and not enough time!!!!!!!!
    Vist my websites - http://pminmo.com & http://millpcbs.com

  6. #6
    Join Date
    Jan 2005
    Posts
    1880
    Is this is why they do star pattern wiring in grounds?????
    thanks
    Michael T.
    "If you don't stand for something, chances are, you'll fall for anything!"

  7. #7
    Join Date
    Mar 2005
    Posts
    1136
    so its D-E that shouldn't be there, and why would it if its opto isolated, correct?

    opto isolator boards (yours being the one I know the best) have the port's negative pins only connected (through the opto isolators) with other port pins. this is being the case, and so long as someone doesn't connect the parallel port ground to the ground in any way connected the with controllers/motor/etc power supply ground, there should not be an issue.

    I want to make sure I understand exactly what the pitfall is you were referring to in the first post, else I am a strong candidate for falling in it thanks for the help

  8. #8
    Join Date
    Jun 2003
    Posts
    3312
    Miljnor,
    Correct, star grounding reduces the opportunity for ground current influence. Everything comes from the center of the star 0V.

    Mcgyver,
    Correct, how you defeat the isolation is having that segment in via a path from one of the db25 ground pins to your electronics/motor/powersupply 0V. With an opto isolator the led source of the isolators current path/loop if from an isolated DC source through the led, through the parallel port output. The isolated dc source is referenced to the PC pport ground.
    Phil, Still too many interests, too many projects, and not enough time!!!!!!!!
    Vist my websites - http://pminmo.com & http://millpcbs.com

  9. #9
    Join Date
    Oct 2003
    Posts
    170
    Thank you Miljnor for clarifying this for our users. Yes, this is why the Star powering is so important. I had to learn the hard way years ago. I just could not believe it made that much difference in a foot of nice heavy copper wire, but it can.

    Tom Eldredge
    Rutex LLC
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  10. #10
    Join Date
    Oct 2003
    Posts
    170
    Gentlemen,

    I now have the wiring diagram for the R2030 drive/Sanyo D. drive connections from Vladimir, which should save time for anyone hooking up any of the Sanyo D. drives. I don't know how to get it into this forum, so if you want a copy of the pdf just email me at [email protected] and I'll attach it with a return email.

    Tom Eldredge
    Rutex LLC
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  11. #11
    Join Date
    Oct 2003
    Posts
    170
    Gentlemen,

    By the way, I have been shipping the R2030 drives and hope to have some feedback from the first users soon.

    Tom Eldredge
    Rutex LLC
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  12. #12
    Join Date
    Dec 2005
    Posts
    3319
    DO NOT BELIEVE THAT OPTO ISOLATION IS NOT CRICICAL!!!!!

    I have a Fanuc 5 controller on my nc lathe (3 actually). The idiot who I bought it from crafted up a BTR between it and the PC. Ground was ground as far as he was concerned so he tied the ground pins of the parallel to the ground interface for the BTR connect of the Fanuc. Turns out that he did the same for all 3.

    The transformer the NC was on was at a different ground potential than the "ground" the PC was on for god knows what reason -(old building, kluged up wiring, whatever).

    Result: the PC fried a number of the horribly obsolete TTL interface chips on the Fanuc due to a ground current issue. Let the smoke out of a number of chips REAL quick when that happens...

    Trying to get an obsolete 1979 motherboard serviced in 2005 ain't easy. Fanuc wanted something like $4500 for the board (yeah sure - paid that much for the whole lathe). Found a guy in Texas who services them at a very reasonable price (considering) but it still cost several thou to fix them.

    Yes, you can run non isolated interface 'tween the PC and whatever. I learned my lesson and WON'T EVER DO IT AGAIN. You are free to ignore this suggestion but you'd probably be less than intelligent/well informed to ignore it.

  13. #13
    Join Date
    Jun 2003
    Posts
    3312
    NC Cams,
    You hit precisely the pitfall of not using isolation. Like I said it isn't a must, but you need to know what you are doing. If you don't you will run into exactly what you said. If you do understand, it's not an absolute have too. As exampled by why the parallel port was created, printers. Old big fast printers (not desktops), didn't have opto isolation. But the printer designer knew how to handle it.
    Phil, Still too many interests, too many projects, and not enough time!!!!!!!!
    Vist my websites - http://pminmo.com & http://millpcbs.com

  14. #14
    Join Date
    Mar 2005
    Posts
    39
    Guys,
    This tread was not intended to be critical of others, whether they prefer a breakout board. I would like to see those that are using them and post what they are using and how they rate them.i.e. ease of setup, functionality, do they seem to be compatible with the Rutex, etc... Also tell what Rutex setup they are in use with.
    Richard

  15. #15
    Join Date
    Jan 2005
    Posts
    1880
    Most of the cheaper BOB boards that I've seen up close only have opto isolation on some of the pins.

    Why is this???

    do you only need opto iso on the outputs from the computer or is this the most likely problem area??
    thanks
    Michael T.
    "If you don't stand for something, chances are, you'll fall for anything!"

  16. #16
    Join Date
    Jun 2003
    Posts
    3312
    Rkonnen,
    My apologies, I believe unintentionally I kind of hijacked what you wanted from your thread. My original post was stricktly do give you some info on your original statment-:"parallel port isolation, he has said that it does not seem to matter". And the simple answer is it may or may not. As to how this thread got off topic, to those wanting more information. I've decided it might be a good topic that fit's my website so I will take part of my posts here and start it. If you have questions go there:
    http://www.pminmo.com/phpBB/viewforum.php?f=13
    Phil, Still too many interests, too many projects, and not enough time!!!!!!!!
    Vist my websites - http://pminmo.com & http://millpcbs.com

  17. #17
    Join Date
    Aug 2005
    Posts
    88
    I have a port question. I am using the non-isolated mother board with three axis of servo drives. I have been successful at getting the drives up and running and the inputs for the limits working as well. I am ready to start on the output side, but I am reluctant for fear of pretty fireworks. I have several Opto-22 240D25 SSR's 3-32 VDC on the control side. I would like to use to run a coolant pump, etc. Can I hook these directly to the motherboard output pins? Theses run straight to the port according to the documentation. I have been unable to ascertain what the current draw for these are. The documentation doesn't say, that I can tell.

    Vince

  18. #18
    Join Date
    Dec 2005
    Posts
    3319
    Until or unless you:

    1. can reverse engineer your interface board
    2. find documentation for same

    It is NOT a good idea to think that any interface board will either sink or source the current necessary to drive real world harware. Since you can't see electrons, you simly can't trust them

    Suggestion for all folks who are looking to use the parallel port to interface with ANYTHING:

    Obtain the book "Real World Interfacing With Your PC", published by Prompt Publications. ISBN 0-7906-1145-7

    This book will to a lot to prevent the unleashing of fireworks and/or smoke from well intended but incorrect utilization of the parallel port. )edit follows( How so??? By showing how to create inputs and outputs from parallel ports as well as the necessary amplifiers to drive high current AC and DC circuits.

  19. #19
    Join Date
    Oct 2003
    Posts
    170
    Vince, and others:

    I can appreciate your apprehension regarding opto-isolation of outputs. I have been building and retrofitting CNC machines for at least 5 years now, and I have been using solid state relays for many years for other things as well.

    I checked the specs. on the below relays and they list isolation at 4000 volts. That's plenty enough for me. I have used opto-22 Ssr relays on many machines, and I have never had a problem. I even use them to turn on three phase coolant pumps and three phase gear shifting motors. Just be sure that they are rated heavily enough to handle the motor start up loads.

    If this scares you too much, have the solid state relays turn on a regular relay or contactor, which I have also done many times. They still work as a cheap pc output interface device, even if you use them to turn on a relay or contactor.

    It's your call. If you don't trust my experience level, go it on your own. It won't hurt my feelings. I'm sure someone else out there has another opinion.

    I always set them up so that the pc port has to "sink" or turn the ssr on by grounding out the signal, and I provide 5 volts to the other side of the relay.

    PC ports can sink a lot more than they can source (pull up to 5 volts).

    One final note... I can't speak for laptops, but I think they would do fine as well.

    I can tell from the tone of some of the previous posts that this post will not increase my popularity, but I can't help that. I'm just sharing my experience for the benefit of this forum.

    Tom Eldredge
    Rutex LLC

    Quote Originally Posted by vebers
    I have a port question. I am using the non-isolated mother board with three axis of servo drives. I have been successful at getting the drives up and running and the inputs for the limits working as well. I am ready to start on the output side, but I am reluctant for fear of pretty fireworks. I have several Opto-22 240D25 SSR's 3-32 VDC on the control side. I would like to use to run a coolant pump, etc. Can I hook these directly to the motherboard output pins? Theses run straight to the port according to the documentation. I have been unable to ascertain what the current draw for these are. The documentation doesn't say, that I can tell.

    Vince
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)

  20. #20
    Join Date
    Dec 2005
    Posts
    3319
    My Fanuc's ran fine for years as well until the fateful day a ground current issue developed 'tween the pc and the home brewed BTR tied between it and the Fanuc mother board.

    A 13 volt differential between the grounds toasted the 74367's on the Fanuc when the grounds got connected and a current started to flow due to said voltage potential difference.

    By isolating the grounds this stopped - the guy who did the BTR figured "ground is ground". He maybe can fix VCR's but his lack of knowledge about grounding ultimately fried the Fanuc's M/B. You, we anybody can get away with non-optoisolated connections for a long time.

    Then one fateful day..... Like I often say, you can't see electrons thereforr you can't trust them

    It isn' the sink or source issue that fried my system - it was TTL talking to TTL. It was the G/D ground current.

    A laptop (not hooked to a power cord plugged into the wall and running on batteries) doesn't/can't have ground current potential issues because the computer ground automatically assumes the ground of the CNC when they get tied together.

    However, plug in a power cord and unknowingly have "ground" not "ground" due to issues outside your control (IE: bad ground at power pole as was our case) and you could be in for an expensive lesson.

    I believe you but do you believe me????