    rs232 issues with a fanuc 6t controller

    Hi All,


    I have a problem that when I connect up a fanuc 6t to a computer rs232 port neweere than a 486 I get a rs232 error even though the port settings are identical 7,2,e . Is there some magic that needs to be done to make newer rs232 ports act like older ones?

  2. #2
    Join Date
    Mar 2003
    Posts
    2932
    What error are you getting?

  3. #3
    Join Date
    Jul 2008
    Posts
    3

    error

    the error is
    86:Reading output by the rs232 interface , a transmission or I/O device problem occured.

    this happens as soon as we bring 6tb-2


    input read on the console of the CNC with the 6tb-2 controller in it. However if the connection is to a older computer (anything less that a pentium) it works and does not give a RS232 error.

  4. #4
    Join Date
    May 2008
    Posts
    16
    Hi,

    The newer PC's have FIFO (First In First Out) buffers on the serial port chips. Fanuc
    systems have a very small buffer (about 12 characters). If the Fanuc issues an XOff
    and the transmission is not halted prior to filling the Fanuc buffer the control will issue
    an error.

    You can disable the FIFO buffers on most serial ports by going to Control Panel, System,
    Hardware Tab, Device Manager, Right Mouse Click on the Serial port and select Properties.

    Go to the Port Settings Tab and press the Advanced button. If the serial port has
    FIFO buffers, uncheck the Use FIFO buffers checkbox.

    If that does not work, you may have to change your communications program on the
    PC to one that uses a polling method for transfering files.

    Hope that helps

  5. #5
    Join Date
    Jul 2008
    Posts
    3

    Serial troubles continue

    Hmmm good info to know, didnt/seem to help it for sure is the hardware because I dont even fire up the mastercam software (or the custome software we have written). As soon as the General Numeric CNC is put into read mode we get the serial error

  6. #6
    Join Date
    Sep 2005
    Posts
    767
    The Fanuc will throw an alarm 086 if it does not see a "high" signal on pins 6 (Data Set Ready) and on pin 8 (Data Carrier Detect). Normally, we just wire the cable so the pins 6, 8, and 20 are all jumpered together on the Fanuc side. Pin 20 on the Fanuc is an output signal (Data Terminal Ready). When you press PUNCH or READ on the Fanuc, it turns on pin 20, which then turns on pins 6 and 8 through your jumper. Problem solved.

    If you're using a commercially made "Nul Modem" cable, or a Nul Modem adapter of some kind, you probably don't have a jumper from pins 6 & 8 to pin 20. Instead, your cable probably connects pins 6 & 8 on the Fanuc side with the DTR signal on the PC side. If this is the way you're wired, then you must open the COM port on the PC side before trying to PUNCH or READ on the CNC side. If the DNC software does not have the port open, you won't get your DTR ready signal, and pins 6 and 8 on the Fanuc will be off, so you'll get the alarm.

    Here's the cable wiring diagram that works for us:

    Fanuc side (25-pin male) ---------------- PC side (9-pin female)
    pin 1 --------------- cable shield
    pin 2 ------------------------------------- pin 2
    pin 3 ------------------------------------- pin 3
    pin 5 ------------------------------------- pin 7
    pin 7 ------------------------------------- pin 5
    pin 6 -----
    pin 8 ----- <-- jumper together
    pin 20 ----

    Alarm 086 is almost always due to pins 6 or 8 not being on. Alarm 087 is usually the "Buffer overflow" alarm that happens because of the FIFO buffer problem mentioned by Vega_Bill

Similar Threads

  1. Fanuc 0P-C controller RS232 Parameters
    By scottsr60 in forum Fanuc
    Replies: 6
    Last Post: 12-30-2014, 11:39 AM
  2. Controller issues, in the home stretch
    By bp092 in forum Gecko Drives
    Replies: 4
    Last Post: 03-18-2008, 10:41 PM
  3. PIC 18F Controller Issues
    By Katratszi in forum Open Source Controller Boards
    Replies: 9
    Last Post: 11-12-2007, 08:00 AM
  4. RS232 connection issues to Milltronics Partner V
    By Jeff S in forum Milltronics
    Replies: 3
    Last Post: 03-16-2007, 12:34 PM
  5. Controller issues
    By Selmac in forum DNC Problems and Solutions
    Replies: 7
    Last Post: 09-25-2006, 05:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •