587,207 active members*
2,986 visitors online*
IndustryArena Forum > CNC Electronics > CNC Machine Related Electronics > Grounding Stepper Motor Driver Wires
Results 1 to 12 of 12
    May 2009
    1333
    On a stepper motor driver we have the high voltage section where we connect the required power and we also have the signal section where the wiring from the stepper motors connect.
    I use shielded cables for both the high voltage and signal sections and my question is do I ground the shielded cable in both sections or just the high voltage or signal section?
    Right now only the shielded cable ground wire from the high voltage section goes to my star point ground.
    Nicolas
    15362
    Re: Grounding Stepper Motor Driver Wires
    Quote Originally Posted by kolias View Post
    Any Ac Power Grounds are separate from Shield Grounding, and should never share the same connection points
    For the shields to have any use at all they need to be clamped to the Ground Plane at Both Ends, Signal shielded wires in some cases can be Grounded (Clamped) at the source end, if you were to have any interference problems
    A P-Clip is one of the best ways to clamp a Shield to the Ground Plane, this needs to be a tight clamp when fastened
    Here are some snips of how it should be done
    Mactec54
    May 2009
    1333
    Thank you mastec54,
    I’m not aware what is “Ground Plane”, can you please explain?
    Nicolas
    May 2009
    1333
    Reading about Ground Plane it’s get more confusing. So in my cnc control panel (about 20”x20”x 9”) I have the 4 stepper drivers, 3 PSU’s and a BOB along with ESS. If I get a piece of metal 3”3”x1/8” thick would that be considered a Ground Plane? If not, any suggestions?
    Nicolas
    Dec 2003
    24223
    Here is two definitive papers on grounding and bonding by Siemens.
    I have used these methods over the years with no kind of problems experienced.
    See the one on shield grounding that has changed when carrying out equi-potential bonding of the earth conductors.
    Attached Thumbnails Attached Thumbnails CNCgndSiemens.pdf   Equi-potential_1.PDF
    Albert E.
    15362
    What is everything mounted on, this is normally a Metal Panel and unpainted wherever anything is mounted this must be paint free
    The Ground Bus is attached to the Ground Plane, (Ground Bus is where all Grounds connect Star Ground) so in your cabinet the Ground Plane is the metal panel that everything is mounted on
    Outside the Cabinet the machine is the Ground Plane, the machine and the Cabinet are Grounded Bonded together from the Ground Bus to the Machine
    So, the Ground Plane can be any part of the machine or cabinet if correctly wired
    If not done this way nothing would be safe to use
    Mactec54
    May 2009
    1333
    Thank you Al for the information
    Nicolas
    Dec 2003
    24223
    "Ground Plane" does not refer to a single physical entity, it is the electrical continuity of all the metallic parts of the machine that are at the same earth GND potential.
    Albert E.
    May 2009
    1333
    Now it is all clear, many thanks to both
    Nicolas
    Jun 2007
    3734
    Yes. All shields terminated at one end only, your star point. If second end not connected no current can flow in the shield and induce currents in enclosed wires.
    Dec 2003
    24223
    Quote Originally Posted by neilw20 View Post
    That used to be the original criteria for shielded cables, read Ch6 of the Siemens Motion Control I posted.
    With the original introduction of low voltage control systems, ground bonding of the machine was not carried out, consequentially it was found that grounding both ends of a shield caused ground loops to occur. imposing current in the shield.
    The problem is that although eliminating ground loops, the shield grounded at one end makes for a good antenna !!
    Now it is recommended that with equi-potential bonding, this eliminates any variation of ground voltages in the system, therefore allowing the ground bonding of both ends of the shield, as per the Siemens recommendation.
    Albert E.
    15362
    No That is incorrect Shields need to terminate at Both Ends, in most cases, or they are become ineffective, these sips pretty much sums it up as to how Shields need to be Terminated
    You must never terminate a shield direct to a Ground Bus (Star Ground Point)
    Mactec54
  1. How do I wire a stepper driver with only 3 wires
    By TTalma in forum Stepper Motors / Drives
    Last Post: 12-01-2018, 09:53 PM
  2. Berger Lahr 5 phase stepper(10 wires), what driver to use
    By giveinfo in forum Stepper Motors / Drives
    Last Post: 09-29-2009, 10:09 PM
  3. stepper motor with 8 wires
    By genije in forum CNC (Mill / Lathe) Control Software (NC)
    Last Post: 08-31-2008, 09:18 PM
  4. stepper motor with 4 wires
    By shauttra in forum Stepper Motors / Drives
    Last Post: 04-03-2008, 11:07 PM