Quote Originally Posted by Toinvd View Post
The +10V power for analog input is indeed a output which can deliver a maximum of 20 mA
The return path for it is the GND analog signal common, so between these two terminals there should be 10 Volt pls. check it
I don't know if it's only there when parameter 00-05 is set to 1
I hope you connected the pot in the right way. The fact that your pot go's open could be that it's blown by wrong connecting
Attachment 488582
The picture is from the manual, but shows 12V where 10V should be
Your diagram is incorrect for his VFD Drive, not only the 12v is incorrect, but the Pot rating is also incorrect, his VFD Drive specs has already been posted, yes it should be an output which is normal for most VFD Drives his +10v output has failed.