587,231 active members*
4,249 visitors online*
IndustryArena Forum > CNC Electronics > Viper Servo drives > supermax YCM-40 to Mach3
Page 4 of 5 2345
Results 61 to 80 of 82
  1. #61
    Nov 2005
    93
    I can have only the Campbell board powered up and reset the button and as soon as I start the VFD, it triggers an E-stop. Tried moving the BOB away from the VFD but still happens. Any Ideas?
    YCM-40 converted from anilam to Mach3 and lovin it.
  2. #62
    Feb 2007
    966
    You can put a .047 uF cap across each limit input right at the BOB.
    If the input is just a non filtered TTL input , it will be sensitive to noise coming in on limit switch wires.
    LK
  3. #63
    Nov 2005
    93
    LK, You hit the nail on the head. after checking voltages and doing a bunch of re-wiring to re-confirm correct 220v 110v and stray ground loop voltages I finally found about 30 volts of induced current in the wiring to the limit terminal E-stop switch that turns the contactor on for the VFD, and also triggers an E-stop in Mach3 through the same shielded cable going into the aux limit input on the BOB. Going to run a separate cable for the 110v and the limit input and install the .047uf caps as insurance. Also in checking all of this, I noticed that the BOB Led's at the step and direction outputs would actually glow when I turned the output of the VFD on (actually running the spindle and doing nothing else) so I'm going to move the BOB away from that "RFD sprayer" Thanks again very much for pointing me in the right direction. Wayne
  4. #64
    Nov 2005
    93
    After running a relay for the contactor instead of running the 110v up to the ESD switch no more e-stops! Now on to figuring out how to control the VFD with the Campbell BOB plus. Wayne
  5. #65
    Jun 2012
    Hello there I want to convert a super max ycm-40 to Mach3 can you helpme please I want to use the original servo motors a all ready have the encoders from USdigital 1000 CPR , 5v
    Miguel
  6. #66
    Jun 2012
    Can some one tell me the experiences in covert the YCM-40 to Mach3 ? What is the best breakout board , the best servo drive ??? Can I use my original transformers ??? Can I skep to buy the hitachi x200 inverter ???
    Thanks to every body
  7. #67
    Jun 2012
    Supermax ycm-40
    Quote Originally Posted by Miguel-2012 View Post
    Miguel
    Super max ycm-40 to mach3 convert
  8. #68
    Mar 2005
    271
    I would go with the Viper Drives from Larry at Larken.
  9. #69
    Nov 2005
    93
    And the Campbell board the original transformer and servo motors as well as the original 12v transformer. Can pretty much everything else except wiring and read read read. I tried to document all of my conversion and will help as much as I can but will probably not answer information that is already here. The best thing to do is pick the drives and BOB then find someone on here with the same setup and read all of their posts and take notes and look at pics. HTH
  10. #70
    Feb 2010
    3447
    Quote Originally Posted by CATCH22 View Post
    I second the VIPER drivers. I have them and use them. Work wonders.
    Also, cnc4pc.com Arturo is REALLY helpful.
  11. #71
    Jan 2006
    204
    update on your machine
    how about an update on your machine how it has been performing what you have been making pictures I am getting started on the Big bridgeport finally
    archie =) =) =)
  12. #72
    Nov 2005
    93
    I will try to get some pics but haven't had a lot of time to work with it although what i have done with it has been faultless. YouTube ycm40 Mach 3 and there is video of the last I cut I believe. I will upload the cutting of the flanges I made for my ls1 engine tomorrow if they're not there already.
  13. #73
    Dec 2012
    Smile CNC Router kitsWantai stepper motor
    hi, maybe you can visit Stepper motor|Stepping gearmotor wholesale|Stepping motor supplier for help.
    Kaly
    MSN: [email protected]
    Skype:kalyred
  14. #74
    Jan 2009
    77
    Two thumbs up for Viper drives & LK BOB, my only regret is that I didn't get it done sooner. Once I really got started last December with the electronics it went much faster than I really expected it to. A lot of mistakes on my part but none with the hardware / software. Made my first few parts with in in February, I'd promised MLW that I would take care of this eyesore first, leftover from rewiring the house over a decade ago;
    Before,
    After,
    2 trials to get to a good one;Click image for larger version.
ID:	178499, Click image for larger version.
    Double sided tape from the Dollar Store worked out OK.
  15. #75
    Feb 2010
    3447
    The only part i don't like about them is the servo tuning. It's way to barbaric.
    Quote Originally Posted by Dstamp View Post
    Before,
    After,
  16. #76
    Jan 2009
    77
    I won't pretend to have mine perfectly tuned, but they're calm and stable. I'd worked with a Westamp driven Thermwood 5-axis a long time ago and when they got out of tune there could be hell to pay, shuddering and bucking until e-stopping itself; occasionally going into fault mode and doing a rapid to the limits / hard stops. With that experience in mind I've taken it pretty slow in terms of optimizing travel speeds. 25 inches per minute is as fast as I've gone with it so far, snails pace compared to current technology but good enough for my basement workshop.
    My total into it is about $2500, $1000 for the machine, $200 for a moving truck, a little under $1000 for the electronics & $300 for some tooling. Spindle spline makes a lot of racket, but it works.
  17. #77
    Jan 2009
    77
    No problem, did you select a breakout board yet? I found it easiest to use the one from Larken, as I used viper drives from Larken also.
    This is the arrangement I used as finished,
    but I found it easiest to debug in this arrangement,
    It started like this, as I was trying to wrap my mind around what to do,
    And this,
    In retrospect, I would have saved a lot of time had I just bought low voltage power supplies instead of salvaging parts from the old control to make do.
    I remembered what I learned in te navy about these solder cup style connectors,
  18. #78
    Jan 2006
    204
    Very similar mill retrofit in progress.
    My Build thread is here.
    Archie's first cnc machine Bridgeport R2E4 Boss 9 to Mach 3
    I started some time ago. If I were starting today I would use the larkin drives and a CNC4PC C32 BOB and the largest torridal transformer cnc4pc has for the drives (I am re using the servo motors and encoders on my mill)
  19. #79
    Feb 2010
    3447
    Quote Originally Posted by jeep534 View Post
    If i did it again, i also would stick with sourcing everything from larken for ease of tech support. I went with a cnc4pc BOB, and electronics + vipers.
  20. #80
    Jan 2006
    204
    Quote Originally Posted by diyengineer View Post
    I really like larkin and his drives. they are really nice however, I don't believe his breakeout board has provisions for the safety charge pump or speed control of the VFD (other than just and on and off signal) pendant or touch probe input support unless I am missing something.
    archie =) =) =)
Page 4 of 5 2345
  1. Yci Supermax
    By krustykrab in forum Hard / High Speed Machining
    Last Post: 10-18-2011, 02:56 AM
  2. CNC Update Log - SuperMax YCM-40 (Anilam to Mach3)
    By radioactive in forum Vertical Mill, Lathe Project Log