    Wiring PCNC1100 To 3-Phase

    Hello guys - any electrician out there who can help answer this?

    Just bought a Tormach PCNC 1100 (used), trying to wire it up and realized my office has industrial 3-phase power (as oppose to residential split-phase 120/240v). On residential power, if you connect the two "hot" legs, because their phase is 180 degrees offset you get double the voltage (240v). But on 3-phase, since the phase offset is 120 degrees, you get 208v (120v x square-root of 3). We also did not have a "wild" leg, meaning any combination (black+red, black+blue, red+blue) all reads 208v, and any legs against neutral (black+white, blue+white, red+white) reads 120v.

    The question is, if I run the PCNC1100 from two of the legs that reads 208v, will it shorten the life of the machine? I am not that much concerned about voltage, the documentation says "200-240v single phase", so 208v is sufficient plus worse case scenario a buck-boost transformer is only like $200 installed. However, since the two phases are not 180 degree offset, I am wondering if I still get perfect sine-wave, or more importantly would it have detrimental effects on the mill over a long period of time.

    Just so you know, I contacted Tormach and they didn't have a clue what 3-phase power is... I was told all I needed is a buck/boost transformer, however the fact that they have never heard of 208v left me a bit skeptical. A 2nd opinion from qualified electrical engineer or electrician would be wonderful!!

    Thanks,



    Wallace

  2. #2
    Join Date
    Feb 2006
    Posts
    7063
    If the machines data plate indicates 200-240VAC is OK, then you'll be fine. The waveform between any two legs of a 3-phase line will still be a perfect sine wave.

    Regards,
    Ray L.

  3. #3
    Join Date
    Jul 2005
    Posts
    34
    The buck boost recommendation is well founded. The machine will work without damage to it at 208, but the VFD that is in the machine does not generate rated torque without a boost to higher voltage. I believe most buck boosts will get up to 239 from 208. We run two 1100s at commercial locations with buck boost transformers. It's worth the small expense.

  4. #4
    Join Date
    Apr 2008
    Posts
    24
    I may have answered my own question... from this post:
    explain 120/208v - Page 4 - Electrician Talk - Professional Electrical Contractors Forum
    (which is part of this thread: explain 120/208v - Electrician Talk - Professional Electrical Contractors Forum)

    It seems the combined sine wave drawn from the voltage differentiation on any 2 phases of a 208v 3-phase power is indeed a pure sine wave. Meaning if I run two of the legs I will effectively have a single phase 208v, pure sine-wave power. Anyone care to kindly confirm?

    Cheers,



    Wallace

  5. #5
    Join Date
    Apr 2008
    Posts
    24
    Quote Originally Posted by HimyKabibble View Post
    If the machines data plate indicates 200-240VAC is OK, then you'll be fine. The waveform between any two legs of a 3-phase line will still be a perfect sine wave.

    Regards,
    Ray L.
    Excellent, thank you for the confirmation!


    Quote Originally Posted by byellin View Post
    The buck boost recommendation is well founded. The machine will work without damage to it at 208, but the VFD that is in the machine does not generate rated torque without a boost to higher voltage. I believe most buck boosts will get up to 239 from 208. We run two 1100s at commercial locations with buck boost transformers. It's worth the small expense.
    Ok that's good to know, this way I can start running some tests and get the machine setup before the buck/boost transformer arrives! One question - if I calibrate the spindle speed now, would it change once we boost the voltage to 240v?



    Thanks guys - I am loving this forum!

  6. #6
    Join Date
    Jul 2012
    Posts
    0
    that is correct.

  7. #7
    Join Date
    Dec 2003
    Posts
    24223
    Using two phases of a three phase supply (without reference to a star neutral) IS effectively single phase.

    Quote Originally Posted by WallaceLau View Post
    On residential power, if you connect the two "hot" legs, because their phase is 180 degrees offset you get double the voltage (240v). But on 3-phase, since the phase offset is 120 degrees, you get 208v (120v x square-root of 3).
    Wallace
    True, 208v, but when using 2 phases without the Neutral reference, the difference is 180° also.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  8. #8
    Join Date
    Feb 2006
    Posts
    7063
    Quote Originally Posted by byellin View Post
    The buck boost recommendation is well founded. The machine will work without damage to it at 208, but the VFD that is in the machine does not generate rated torque without a boost to higher voltage. I believe most buck boosts will get up to 239 from 208. We run two 1100s at commercial locations with buck boost transformers. It's worth the small expense.
    Torque comes from current, not voltage. Reduced voltage will, if anything, reduce maximum RPM.

    Regards,
    Ray L.

  9. #9
    Join Date
    Dec 2003
    Posts
    24223
    Quote Originally Posted by HimyKabibble View Post
    Torque comes from current, not voltage. Reduced voltage will, if anything, reduce maximum RPM.

    Regards,
    Ray L.
    The only thing I would question there is that with an induction motor the RPM is a result of frequency, because this is produced artificially in the VFD, the max frequency will be the same.
    In this case if the voltage is lower the wattage capability will be down.
    Very similar to running a 3ph motor direct off of 3ph, if the motor is rated at 220 and it is run off of 208, it will still run up to the Same Frequency, just that the slip frequency will be affected slightly for the same load.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  10. #10
    Join Date
    Jun 2006
    Posts
    3063
    For what it is worth, Tormach appears to sell a transformer for this purpose:

    32554 - Buck-Boost Transformer

    $115 doesn't seem too bad to me, for a little peace of mind.

    Mike

  11. #11
    Join Date
    Apr 2008
    Posts
    24
    Great and thanks for all the reply! I learn something new everyday. :-)

    By the way, Mike, thanks for the link! I know Tormach offers a transformer but I didn't think their price would be any good, turns out I was wrong! McMaster wants $136 for the same 500VAC unit, plus tax and shipping. I guess I will be sending more business to Tormach...

    For now I will start running the mill and get everything setup (leveling, gib adjustment, etc). May have to buy a gauge to adjust tram... and the real fun should begin once the transformer is installed. Wohooo!



    W.

Similar Threads

  1. 3 phase motor wiring...
    By REVCAM_Bob in forum Phase Converters
    Replies: 22
    Last Post: 10-11-2011, 05:58 PM
  2. three phase wiring with only a N for 120
    By chimpera in forum CNC Machine Related Electronics
    Replies: 10
    Last Post: 09-04-2011, 06:08 PM
  3. What's the difference between 2 phase and 4 phase wiring?
    By David Bord in forum Gecko Drives
    Replies: 0
    Last Post: 09-01-2010, 09:37 PM
  4. 5 phase stepper wiring
    By Bambang Otto in forum Stepper Motors / Drives
    Replies: 0
    Last Post: 10-27-2009, 10:35 AM
  5. help wiring 1 phase motor
    By ezland00 in forum CNC Machine Related Electronics
    Replies: 7
    Last Post: 05-15-2006, 10:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •