Hello guys - any electrician out there who can help answer this?
Just bought a Tormach PCNC 1100 (used), trying to wire it up and realized my office has industrial 3-phase power (as oppose to residential split-phase 120/240v). On residential power, if you connect the two "hot" legs, because their phase is 180 degrees offset you get double the voltage (240v). But on 3-phase, since the phase offset is 120 degrees, you get 208v (120v x square-root of 3). We also did not have a "wild" leg, meaning any combination (black+red, black+blue, red+blue) all reads 208v, and any legs against neutral (black+white, blue+white, red+white) reads 120v.
The question is, if I run the PCNC1100 from two of the legs that reads 208v, will it shorten the life of the machine? I am not that much concerned about voltage, the documentation says "200-240v single phase", so 208v is sufficient plus worse case scenario a buck-boost transformer is only like $200 installed. However, since the two phases are not 180 degree offset, I am wondering if I still get perfect sine-wave, or more importantly would it have detrimental effects on the mill over a long period of time.
Just so you know, I contacted Tormach and they didn't have a clue what 3-phase power is... I was told all I needed is a buck/boost transformer, however the fact that they have never heard of 208v left me a bit skeptical. A 2nd opinion from qualified electrical engineer or electrician would be wonderful!!
Thanks,
Wallace