    With the power off you can also check resistance for 0 ohms from the top of the O/L terminal to the corresponding bottom terminal. Some O/L's are mounted separate to the contactor, others are integral, but same function.
    With the contactor non-activated the reset should stay in, and only possibly pop back out when the contactor is picked up, if overload exists.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  2. #2
    Join Date
    May 2013
    Posts
    10
    I just did what you suggested (with the power off), and am getting a reading of 2 ohms between corresponding terminals (it is an integral O/L). What does this mean? and what would you suggest next?

  3. #3
    Join Date
    Dec 2003
    Posts
    24260
    0v to 2 ohms looks right.
    O/L = over load.
    (Alarm 90-4) "Coolant motor overload protection has tripped.

    Somewhere it has to get this information and is usually the N.O/N.C. monitoring contacts on the O/L.
    These are low voltage inputs into the controller?
    You could also see if the the one(s) that are wired are registering open or closed, or opposite to what they are labeled (tripped state).
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    May 2013
    Posts
    10
    N.O./N.C. contacts? Where are these located. I'm sorry I'm new to all of this and don't know the technical terms/abbreviations a whole lot.

    I attached some photos of the controller I'm working on. The red switch on the right is what I'm assuming to be the trip.

    Attachment 186332Attachment 186334

Similar Threads

  1. Tm Coolant Pump
    By behindpropeller in forum Haas Mills
    Replies: 1
    Last Post: 03-15-2010, 04:45 PM
  2. Fanuc OM Thermal Tripped error
    By Singlehick in forum Fanuc
    Replies: 1
    Last Post: 12-07-2008, 11:40 PM
  3. coolant pump
    By JACKSMACHINE in forum Fadal
    Replies: 0
    Last Post: 05-22-2008, 09:13 PM
  4. TM2 Coolant pump
    By Peter Gibbs in forum Haas Mills
    Replies: 4
    Last Post: 05-03-2008, 06:11 PM
  5. Coolant Pump
    By Smackre in forum Mechanical Calculations/Engineering Design
    Replies: 7
    Last Post: 06-29-2007, 07:16 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •