FANUC parameters will not control the buttons on the operator panel. Those will be control by PMC parameters or Diagnostics. These will not be in any FANUC manual.
FANUC parameters will not control the buttons on the operator panel. Those will be control by PMC parameters or Diagnostics. These will not be in any FANUC manual.
Thanks I contacted the machine builder and they supplied me with a list of PMC parameters. However I can't find where to put them in on the controller?? Does anyone have the procedures for this? I have never had to replace parameters in a machine before and I'm lost as to where these ones go. I have paged through my parameters both in the parameters page and the diagnostic page and can't find anything that looks like the list I have.
What does your list look like? Most PMC parameters start in the DGNOS at 300.
The list they sent starts at N10300 and goes to N10399. I'm assuming they represent numbers 300-399. But in the control lines 310 and 311 are only 1 digit. The list has a normal 8 digit number for the bits. I can input the number in 310 and it enters leaving the preceding zeros out. (00101100 enters as 101100)However when I try to input 311 (00000001) nothing happens. It won't input the number whether I put it in as a 1 digit number or an 8 digit number.
So I can't input these by hand? All I have is a paper printout the company sent me.
You can input by hand. But you need to convert binary to decimal.