Hi
I have a yh-28 lathe with oi tc
it gives a emg alarm and it doenst go away and the emergency switch works normaly
I hope someone can help me
Hi
Check X8.4 and G8.4. Both signals must be on to clear ESTOP
Can you see what in the ladder is preventing G8.4 from coming on? You need to search for the coil in the ladder.
do you have a pdf document with your electrical diagram?
or open the electrical diagram and in 1 page should be the entire emergency circuit,make a photo and post it.
you should check with a voltmeter if you have +24v DC in the emergency stop buttons and on the limit switch for hard travel for all axes.One of these has an interrupt.
show us a picture.If the limit switch is not pressed ,you should have 24v on it.
This is a standard Emergency circuit
Attachment 307126
you have the EMG push button than you have the overtravels 131,132 ,this is from a lathe so 2 axes limit switches,the +24v(L
+) goes in the EMG than goes to the switches and than in a relay and finally to L-.
So is like the christmas tree leds that are connected in serial mode.
all the contacts are normally closed so when 1 of these is open the 24V will not reach the relay so the machine will show alarm and NOT READY state.
the point is you must measure the 24V(L+) checking with the L-.
This is basic electric so i hope you understand it.
good luck.
I am having the same problem, but my F45 will not come on
Hi
i need help regarding 21i mb controller.On i/o card a20b-2002-0521/06A connectors CE56,CE57 i dont know on which pin number having *esp signal.
a1=24v,b1=0v i know that but other pins number which function it have i dont know can anyone help with this problem.
The problem is these connections are variables. That mean it all depends on how the I/O assignments has been laid out. Fanuc states in this example:
Xm+0.0 M= starting address for this address. So if your starting address is X8 this pin would be X8+0.0 or X8.0
Hope that helps.
yes i think you are right but i dont know w to I/O assignment to do from X8.+0.could you please help me. [email protected].
thanks.
Hi!!!
I have a similar problem with a Nakamura Tome TMC-12 Control Series 21-T, this machine was working well, until a technician came to check a vibration in the Z axis servo, apparently it loaded parameters and the machine did not return to work, I have a backup of the machine parameters, I reloaded them, no alarm comes out, but it is in EMG state, I can navigate the menus, but nothing else works (spindle, hydraulic system, turret , move the axes).
Hopefully someone can help me, best regards.