    VFD wire type
    Put this on another forum earlier but this is probably a better place because the other is more of a user group and not a DIY builder focused forum.
    Could one of you sparkie experts educate me?
    Hooking up a new VFD to a new spindle. 220V 3-phase. Have two choices of VFD cable. Which is better?
    1) four conductors, each insulated, with shield wire
    https://www.wireandcableyourway.com/...vfd-cable.html
    2) three conductors (insulated) with three shield wires that touch shield the whole length
    From online reading it sounds like I need to bond the shield to the ground at each end anyway to prevent noise so is that the purpose of the three smaller shield wires that touch the whole length?
    Which option above is better for less noise or is there really that much difference for a fairly short run (50') so just go with the cheaper one?
    Dec 2013
    5716
    Re: VFD wire type
    The less expensive would be fine. Only connect the shield at the panel end to prevent a ground loop.
    EDIT:
    I didn't read the specs very well, you want to use the 4 conductor cable, to keep the safety ground isolated from the shield on the motor end. As above only ground the shield on the panel end.
    Nov 2006
    1036
    Re: VFD wire type
    Do you really need 12 gauge wire? I used 16 gauge on my spindle and that was overkill.
    Dec 2003
    24220
    Re: VFD wire type
    From my experience of installing VFD's over a number of decades, I have never used shielded cable from VFD to motor, for the most part, what I have used is liquid seal metallic flex conduit, with TEW/MTW in the flex, the 3ph conductors need to be twisted together with the ground conductor ran along side them (untwisted).
    This ends up with the conduit, which is essentially a shield, grounded both ends.
    The earth conductor goes to the VFD and continues on to the motor frame.
    the effect of grounding and bonding both ends essentially eliminates ground loops.
    The definition of a ground loop, BTW is when there is a potential difference between one point of ground and another.
    The oldest motor I fitted a VFD to was originally installed in 1959!!
    Al.
    Albert E.
    Mar 2005
    109
    Re: VFD wire type
    How much current is your spindle rated at? Its in the nameplate. I accidentally ordered a 14GAU VFD cable, 4 conductor and mesh shielding and it was a huge diameter cable.
    Based on other member's recommendation and like DonFrambach, I ordered a 16AWG/4C cable from McMaster-Carr at a buck 'n a half per foot. Rated at 18Amp @86° F 600V.
    No-Conduit-Required Double-Shielded Control Cable
  1. What Type Wire?
    By 3Dsigns in forum CNC Wire Foam Cutter Machines
    Last Post: 08-30-2013, 11:34 PM
  2. What type wire?
    Last Post: 11-19-2012, 08:56 PM
  3. Mitsubishi wire type setting for zinc coated wire
    By Futurewire in forum EDM Discussion General Topics
    Last Post: 01-26-2011, 10:47 AM
  4. Mitsubishi wire type setting for zinc coated wire
    Last Post: 01-25-2011, 01:49 PM
  5. Wire EDM - Wire Type and Size
    By greenchair in forum Uncategorised MetalWorking Machines
    Last Post: 06-17-2009, 07:44 PM