Here are the essential Parameters that need to be set, for a trouble free start up
Huanyang Mactec54
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control ) ( J1 Also Needs to be set for Terminal Control )
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220 (Motor Rated Voltage, If you have 120v spindle then set to 120v )
PD009=15
PD010=8
PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Acceleration=12 ( Adjust to suit)
PD015 Deceleration=12 (Adjust to suit) ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
PD142= ( Motor Max Amps)
PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
PD72=400
PD73=120 ( 100 Minimum Setting )