I have been banging my head against a brick wall with this for the last week or so, have done a lot of googling and learnt a hell of a lot about RS485 and modbus at the same time.
And a big lesson learned - don't beleive everything you read! Make you own measurements and checks.
Today was the turning point when I borrowed a USB osilloscope and actually started seeing the data transmission. And the simple solution - SWAP TWO WIRES!!!
The labelling of the RS- and RS+ terminals on the drive and the A and B terminals on the USB converter are not as expected.
Matching the potential of the terminals (relative to ground) was the key, ignoring the labelling. A [+5V] --> RS+ [+5V], B [0V] --> RS- [0V] and Ground -> ACM. The comms still work with the 120ohm termination resistor as well. And SpindleTalker also works as it is no longer receiving the 00 response (which was not coming out of the drive but the converter itself)