    He would need a Neutral wire to get 120v supply from the 240v source
    Depending on what size his spindle Hp is he may not need a RPC for his machine at all, so he needs posts what his spindle requirement's are and does it have a VFD Drive
    The spindle motor is a 5.5 kw 3phase servo spindle motor running a 3 phase pulse/direction drive.
    The servo for my z is also a dedicated 3phase drive.
    So as far as I can tell 3 phase is required.
    So after chatting with Phase Technologies the output is closed Delta 3 wire phase to phase 1% voltage with on leg being high phase to ground...
    The 220v servo drives are currently running 2 hot legs of 220v service no neutral in my test setup( the inputs are designed for oversees power 1 hot 220v leg 1 neutral)
    So could I in theory just run those from 2 low legs to ground with 220v between phase?
    That just leaves me with the 110v issue
    15362
    Re: Getting single phase 220v and 110v from 3 phase 220v
    Quote Originally Posted by PIVOTALCUSTOMS View Post
    You need a neutral for 120v single phase which you can split from any of you main 240v supply if you live in NA then you have120 / 240v single phase supply not 220v
    Don't believe what they are telling you about the RPC, there is not an RPC made, does not matter what brand or manufacture they will not be even close to 1% even the CNC grade RPC
    No you can not run the low legs to Ground lots of smoke and Brakers would trip if you short a live wires of anything
    Now if you where talking Phase Perfect then there digital phase converter can easy give you clean 3Ph power @ 98% efficiency
    Who is the manufacture of the servo drive most 3Ph servo drives will run on single yours would be at the top of the range for single phase though but worth a try
    Mactec54
    Dec 2013
    5716
    You are correct in that you can't buy one off the shelf. But it's possible to build one Here is a picture of the panel meters on mine 1.01% or better under most operating conditions. T1-T3 is about 255 unloaded, but settles right down under any load. But a Phase Perfect would probably be better.
    239, 237, 239, 236 if you can't read the meters.
    Jim Dawson
    Sandy, Oregon, USA
    15362
    Looks good but still not the at 1% if your wild leg is 255 then you are around 6.7% no point in showing something that others can't have or likely to achieve, but still in reality is no better than a CNC rated RPC
    Mactec54
    Aug 2013
    76
    Mactec54 Yes I have single phase 240v. I'm not running the low legs to ground, as I value my life lol. What I am doing is running the 2 hot legs of my 240v single phase to the L and N terminals on my drive.
    Also I was not talking about RPC at 1% I was referring to the phase technologies phase perfect converter.
    Also what you said in regards to passing the neutral through is what I was trying to find out. That's something they offer? If I did that and brought the neutral in then I should be able to run the 110v single between the neutral and one of the non manufactured legs correct?
    There isn't an issue with bringing along the neutral in a Delta configuration?
    15362
    Correct
    I don't know if they offer that but if you tell them what you want to do I'm sure they could add an isolated lug or terminal block for the Neutral wire, or you could do it yourself as well
    No it's not a problem as long as you take your ( 1 ) 120v hot leg from the input Power side of the Phase Perfect and not from the output
    You also could run separate 120v circuit from the power supply panel that is feeding the Phase Perfect, as long as you use the same Ground connection as the Phase Perfect you would be fine also
    Mactec54
    15362
    Are that makes a big difference Phase Perfect is the way to go if you need 3ph power I have a PT380 you could get them to add a Neutral terminal block so you could run a Neutral for a 120v supply as well I did not but did not have a need for 120v
    You would take the 120v from one Hot leg that feeds the Phase Perfect and the Neutral and Ground would give you a normal 120v supply
    Mactec54
  1. Replies: 34
    Last Post: 08-17-2021, 07:16 AM
  2. 110v VFD, 220v, 1 phase, 3 phases - I'm kind of lost
    By Biggs427 in forum Spindles / VFD
    Last Post: 06-16-2017, 02:52 PM
  3. Bridgeport R2E3 delima, 220v VFD 3 phase Versus 220V Single Phase
    By ronderkis in forum Bridgeport / Hardinge Mills
    Last Post: 03-25-2015, 04:01 AM
  4. Replies: 2
    Last Post: 06-20-2014, 05:24 AM
  5. Replies: 12
    Last Post: 10-13-2009, 03:53 AM