    Re: Spindle grounding- manufacturer says to not ground

    Quite common to find that.
    Just to bring a sense of reason, the gantry, mill head etc that is installed on the machine should have an earth ground/bonding conductor to it.
    So the frame of the motor would be earth grounded through the mounting anyway, but it is not wise to rely solely on that method.
    Most remove the 4pin receptacle and fit an earth GND from pin to motor frame. Then use a 4 conductor cable to the motor.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  2. #2
    Join Date
    Dec 2021
    Posts
    9

    Re: Spindle grounding- manufacturer says to not ground

    So the ground terminal on the VFD would have two wires on it, correct? --> One from the spindle ground that I create, and the other on the ground wire for the 220v supply into the VFD... Yeah, I'm pretty new at this..

    I'd like to guess about the Chinese note on causing damage if the spindle is grounded. They refer to the problem being when cutting metal (pretend for a moment that is possible with this spindle). Would they be referring to creating a ground loop? When your cutter engages the material, it would be possible depending on your machine construction that the spindle ground and the chassis ground are connected?

    What kind of damage are we talking about with a ground loop here? Death? Destroying the VFD or spinlde?

    Nick

  3. #3
    Join Date
    Jan 2005
    Posts
    15362

    Re: Spindle grounding- manufacturer says to not ground

    Quote Originally Posted by Norkamus View Post
    So the ground terminal on the VFD would have two wires on it, correct? --> One from the spindle ground that I create, and the other on the ground wire for the 220v supply into the VFD... Yeah, I'm pretty new at this..

    I'd like to guess about the Chinese note on causing damage if the spindle is grounded. They refer to the problem being when cutting metal (pretend for a moment that is possible with this spindle). Would they be referring to creating a ground loop? When your cutter engages the material, it would be possible depending on your machine construction that the spindle ground and the chassis ground are connected?

    What kind of damage are we talking about with a ground loop here? Death? Destroying the VFD or spinlde?

    Nick
    Electrical shock is what you can expect to get with an un-Grounded spindle, the rotor voltage has to go somewhere and if it can't go through a Grounding conductor, then when you touch the spindle to change a cutter you will get Zapped.

    Can this damage a spindle motor No not at all. it is an electrical code requirement to have it Grounded so don't run this until you have all the correct wiring in place that means from the VFD to the Spindle you need a 4-wire shielded cable and the shield correctly terminated at each end with 360 Degree clamp

    You should use a Star-Point Ground stud or Bus in your cabinet all Grounds connect to this one point
    Mactec54

Similar Threads

  1. Grounding router spindle?
    By Mogal in forum DIY CNC Router Table Machines
    Replies: 16
    Last Post: 02-07-2022, 07:32 PM
  2. Spindle/machine grounding
    By amowry in forum Spindles / VFD
    Replies: 3
    Last Post: 02-11-2018, 05:23 PM
  3. Grounding a 2.2kw VFD spindle
    By DDMODS in forum Spindles / VFD
    Replies: 6
    Last Post: 07-21-2016, 11:28 AM
  4. Help!!! Touch probe grounding through spindle???
    By Momentz in forum DIY CNC Router Table Machines
    Replies: 1
    Last Post: 11-28-2014, 10:21 PM
  5. grounding question, PC case ground
    By Fiero Addiction in forum Waterjet General Topics
    Replies: 2
    Last Post: 08-16-2008, 01:40 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •