mactec54
Your spindle Amp rating would be 8.5 to 9Amps would be correct, unless you have set the overload Parameters the VFD Drive will supply up to 200% more than your 9Amp setting, the VFD Drive reading of 4 Amps =12Amps so you have not set the overload to 100% or 110% seems to be safe for these spindles.
The spindle cable shield is incorrectly Grounded, you also have a Ground loop if you have 2 Main AC Power supplies connected to your machine, the line reactor will help a little, the EMI Power Filter is best, reactor is not needed. only a quality EMI Power Filter
The spindle cable needs to be corrected; the shield needs to be clamped to the Ground Plane and clamped at both ends.
For the Machines Main Power supply, would have to see some photos to help you correct it.